Hot Water Tank Vent Rise

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by RazorKing, Oct 24, 2005.

  1. RazorKing

    RazorKing New Member

    Messages:
    4
    Hi Guys! First Post! The name is Dave and I need some advice.

    Just replaced the Hot Water Heater in my residence, SW PA. New tank is Whirlpool, Natural Gas, LoNox, Flameloc, 40 gal, 62" tall.
    I vent out of the vent cap with an immediate 3" 90 degree elbow with 5' of horizontal pipe which then necks up to 4" going thru block wall to vertical stack outside house which rises above roof, total height 15/20'.
    Installation instructs calls for .250" rise for every foot of horizontal travel. I just make that requirement but it's there.
    Will this setup give me adequate exhaust and no backdraft?

    Also, is there a simple test to check for proper draft at vent cap? How do I know the system is working properly.

    Thanks!
  2. plumber1

    plumber1 Plumber

    Messages:
    1,423
    Location:
    Florida
    vent

    Light a loosely rolled piece of paper, the blow it out. put it near the vent or flue. It should draft up the stack. If it blows back, your not venting...
  3. RazorKing

    RazorKing New Member

    Messages:
    4
    Thanks 1.
    I tried that last night with wood stick matches. Smoke did not draft into the cap or blow away from in, just floated up. When I moved the match inside the perimeter of the cap it shot up the vent.
    It was cold here last night, low 40's.
    I'm thinking I got it right but just want to be sure because of the minimum rise on the horizontal pipe.
  4. plumber1

    plumber1 Plumber

    Messages:
    1,423
    Location:
    Florida
    vent

    I think you have it too........
  5. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Most manufacturers specify that the flue must rise vertically for a minimum of 6 to 9 inches before the elbow. Placing the elbow where you did can cause too much back pressure. You may have problems with the burner not staying lit.

    Did your inspector accept this installation?
  6. 1/4" per foot or more is legal in your situation. They make a draft gauge that is designed to measure FPM's, Feet Per Minute draw.Most plumbing inspectors in my area require a minimum 300 fpm's draw to be considered safe operation. Most new water heaters and decent flue chases usually pull anywhere from 500 to 700 FPM's.
  7. vent rise

    the vent rise is only half your problems....

    your biggest problem will be in about a year or so from

    now when you cant keep your water heater lit.


    your biggest problem is you bought a FLAME LOCK
    Whirlpool from LOWES and they are nothing but trouble.

    here are the cleaning instructions,
    eventually you are going to need them

    http://www.whirlpoolwaterheaters.com/support/bulletins/6510338.pdf
  8. RazorKing

    RazorKing New Member

    Messages:
    4
    OK, I wish I would have found you guys prior to the purchase, but that was what Lowe's carries and I needed to buy it on a Saturday afternoon!
    The basis for the complaint against this item is basically the blocked intake right? As long as I keep the intake clean I should be good. It came with additional filter that wraps around the base for further protection. Heck, I have to change the furnace filter every couple of months!
    This was a replacement of an exsisting system.
    The height of the heater is 58" compared to a 48" model. Doesn't the additional height of heater assist with the speed of the escaping gases to overcome the quick 90 out of the draft cap. I do have a small vertical pipe installed on top of cap, approx 3"
    Sounds like I need a draft flow meter!
    That's 300 min for just pilot or with burner on?
    And By the Way, I want to Thank you Pro's for getting on these forums to help the weekend warriors. Believe me ! I'd love to call in a pro every time I need something done, unfortuantely economics doesn't allow that, it might if the government wasn't taking so much of the income! Unfortunately we have let the pie get to big and it needs lots of filling!
    Thanks Guys!
Similar Threads: Water Tank
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & pulsatron metering pump for chlorinator is sucking water into solution tank Jul 15, 2014
Plumbing Forum, Professional & DIY Advice, Tips & brand new electric hot water tank water only getting luke warm Feb 1, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Expansion Tank and Water Hammer Arrester Jan 7, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Expansion tank for water heater Dec 21, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Running out of hot water with a 60G tank Dec 8, 2013

Share This Page