hot water runs out QUICKLY

Discussion in 'Water Heater Forum, Tanks' started by ewillyb, Nov 21, 2009.

  1. ewillyb

    ewillyb New Member

    Joined:
    Nov 21, 2009
    Location:
    silver spring, md
    Hello. My hot water starts to run out during a single, normal shower.
    I have a State Industries GS650YBRT-200 50 gal. gas heater that is only 1 year old. I just moved into the house, so I do not know when this problem started.

    What to do? I'm a plumbing newbie. My common sense tells me that turning up the temperature would not help the problem. The water comes out plenty hot at first.

    Call in a professional or are there some things I can check on my own?

    Many thanks,
    Eric
     
  2. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    heater

    Without knowing what the heater's setting is now, it is impossible to tell if raising it would be the cure, but it may very well be.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    The hotter the tank outlet, the less of it you use to maintain the same temp in the shower. The danger is that if you forget, you could scald yourself. The solution to that is to install a tempering valve at the outlet of the WH, this is the equivalent of you mixing in more cold, but it prevents the likelyhood of getting scalded if you forget and open up the hot too much.
     
  5. Runs with bison

    Runs with bison Member

    Joined:
    Aug 23, 2009
    Location:
    Midwest
    How long does it take before the water runs out and what is the flowrate of the showerhead?

    Assuming this is something less than 10 minutes and it is ~2.5 gpm showerhead, then perhaps the dip tube is broken?
     
  6. Gary Swart

    Gary Swart In the Trades

    Joined:
    Sep 1, 2004
    Location:
    Yakima WA
    It does sound like a broken dip tube. That is not a normal thing in a 1 year old heater, but things happen. The dip tube is located inside the water inlet and is easily removed and replaced.
     
  7. hj

    hj Moderator & Master Plumber Staff Member

    Joined:
    Aug 31, 2004
    Occupation:
    Plumber
    Location:
    Cave Creek, Arizona
    heater

    10 minutes with a 2.5 gpm head is 25 gallons, which is about par for a 40 gallon water heater, and even a 50 if the temperature were set at 120 or below. A broken dip tube would produce about 10 gallons before going cold, and would not have any point where it dropped to warm first.
     
Similar Threads: water runs
Forum Title Date
Water Heater Forum, Tanks suddenly water is hotter than normal, but runs cold after 8 min. Feb 7, 2014
Water Heater Forum, Tanks Water dripping from expansion tank Saturday at 9:48 AM
Water Heater Forum, Tanks Two water heaters, two expansion tanks May 19, 2015
Water Heater Forum, Tanks Leaking water heater May 15, 2015
Water Heater Forum, Tanks Add Indirect Water Heater? May 13, 2015

Share This Page