Hot Tub Wiring
Discussion in 'Electrical Forum discussion & Blog' started by aopainter, May 31, 2011.
  1. DonL
    DonL Jack of all trades Master of one
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    It should be on a ground fault interrupt.
    DonL
  2. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    Mixing conductor sizes and colors may be a problem, the ground wire can be smaller, but the other current conductors need to be the same size.
    I hope your project works well.
    Be careful playing with electricity...
    DonL
  3. Jim Port
    Jim Port Electrical Contractor
    Aug 22, 2009
    Maryland
    I would not change to a smaller size neutral. Some tubs also call for a ground the same size as the other conductors.
  4. ActionDave
    ActionDave Electrician
    Feb 4, 2009
    Electrician
    Colorado
    What size breaker are you tying the 6AWG to? I would guess either a fifty or forty amp breaker. That would mean you would need at least a 10AWG green.
    Jim Port correctly states that some manufactures, a lot actually, want a full size neutral and ground. Check your instructions.
  5. aopainter
    aopainter New Member
    May 31, 2011
    Seattle
    It's a 60 amp Disconnect panel
  6. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    Don’t make this more than it has to be.
    Install #4 SE-R al. to the disconnect located on the outside wall and then flex and THW cu. conductors to the tub.
  7. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    I am glad you stopped by JW,
    I don't think that his friend needs to be thrown under the bus, he is trying to help out.
    And aopainter just wants help, not BS.
    Thank You...
  8. ActionDave
    Feb 4, 2009
    Electrician
    Colorado
    10AWG copper will work for an equipment ground up to sixty amp.
    This is another way to skin your cat and would most likely be more economical.
  9. aopainter
    May 31, 2011
    Seattle
    I can't find this cable anywhere online to know what it looks like. I'm going down to the electrical wire store today, so I'll ask about that wire. I was able to get about 90ft of PVC conduit for $17, so i'm going to put that in the attic
  10. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    Save some conduit for exposed wire outside...
    What wire can you not find ?
  11. aopainter
    May 31, 2011
    Seattle
    I bought 20ft of EMT conduit for the outside. But the wire I cant find online is "#4 SE-R al." And thats 4AWG right? Do I need 4AWG, i thought 6AWG was what I wanted
  12. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    If you are putting in a 60 amp service, then you may need #4.
    You might want to see what your current requirements are, and that will determine the breaker and wires size.
    The length does play into the equation, But code seems to play different, That depends on local codes.
    Maybe your friend could make sure that you can meet your code. He should know the requirements.
  13. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    #4 American Wire Gauge aluminum Service Entrance four conductor cable is good for 50 amps. It does not need to be installed in a conduit. Lowe’s or Home Depot will cut to length or any electrical supply house.
    Electrical Metallic Tubing is a bad idea to use for the final connection to the hot tub as the chemicals used in the tub will cause it to rust. Non-Metallic Flex is a better idea for the final run of copper THW conductors.
    Take you age and multiply it by 10 and you haven’t come close to the number of these tubs I have installed in my life time so listen to experience.
  14. Jim Port
    Aug 22, 2009
    Maryland
    The SER cannot be used for the exterior portions to feed the hot tub. The grounding conductor needs to be insulated.
    There is a 6' limit on the flex to feed the tub.
  15. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    JW is correct, old farts know some stuff.....
    Just meet your local code... And get it done...
  16. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    6 feet from the outside of the tub in the 2011 edition
  17. ShockHazard
    ShockHazard New Member
    Nov 1, 2012
    Independent Contractor
    North East Pennsylvania
    Is it legal to have a 3 conductor feed going outside?
    I was under the impression all outdoor 220 fixtures were 4 conductor only.
Similar Threads: Wiring
Electrical Forum discussion & Blog Underground UF Wiring Gauge Selection Yesterday at 7:29 PM
Electrical Forum discussion & Blog Wiring Split 15 & 20 amp circuits on same receptacle Yesterday at 7:05 PM
Electrical Forum discussion & Blog Need help wiring ceiling fan! Feb 15, 2017
Electrical Forum discussion & Blog Strange Dimmer Switch Wiring Jan 6, 2017
Electrical Forum discussion & Blog Doorbell Wiring Dec 29, 2016