    I want to use a common drain for a tub and a shower. The most convenient point to tie the two drains together (each has its own trap) is in the center of the bathroom and I would install a single vent connection just before the two drains join. That would necessitate running the vent horizontally about 10 feet to reach a wall and then turning the vent vertical and taking it through the roof. The horizontal portion of the vent would maintain a 1/4" per foot slope. The IRC applies and the installation is in a one story house.

    A schematic of the proposed piping is available on
    http://s253.photobucket.com/albums/hh75/nculbertyh/
    The santee used for the vent connection would be installed with the vent branch in the vertical position.

    Is there a limit to how long the horizontal portion of the vent can be?
  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    A vent can NOT run horizontal at all until it is 42" above the floor, or 6" above the flood rim of all the fixtures. It must come off the drain via a wye rolled to 45º and continue not less than 45º upward, until the 42" height is reached.
  3. Terry

    Terry Administrator Staff Member

    Messages:
    14,770
    Location:
    Bothell, Washington
    The tub should be vented too, and the two vents tied together above the 42" level.
    Or at the least, 6" above the top of the tub.

    Like Jimbo mentioned, the vents need to be rolled above the flow line of the pipes.
  4. nculbertgm

    nculbertgm New Member

    Messages:
    3
  5. seaneys

    seaneys New Member

    Messages:
    192
    Location:
    Chicago Suburbs
    I must be missing something. How would you vent any floor drains that are next to a wall (say a shower drain that is centered in a 40x48 shower)? Wouldn't you have to run horizontal for a few feet until you can shoot up into the wall?
  6. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    The trap arm runs horizontal, typically to a vertical tee, and the vent comes off vertical. If the vent must be taken off a horizonal pipe, it is done with a wye rolled to a 45º and the vent pipe must rise at least at 45º until it is above the flood rim of fixtures.
  7. seaneys

    seaneys New Member

    Messages:
    192
    Location:
    Chicago Suburbs
    Argh....

    Illinois Plumbing Code:

    b) Vertical Rise. Where vent pipes connect to a horizontal soil or waste pipe, the vent shall be taken off above the center line of the soil or waste pipe, and the vent pipe shall rise vertically, or at an angle not more than 45 degrees from the vertical before offsetting horizontally or before connecting to the branch vent. (See Appendix K: Illustration G.)
  8. seaneys

    seaneys New Member

    Messages:
    192
    Location:
    Chicago Suburbs
    If you are draining into a horizontal line, could the vent be taken off upstream of where the trap arm connects?
Similar Threads: Horizontal vent
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & What is the maximum length for a horizontal "foot" vent connection under UPC? May 4, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Can I connect a 10' horizontal pipe to a vertical venting pipe? thanks Mar 20, 2014
Plumbing Forum, Professional & DIY Advice, Tips & How soon can the vent from a roof drain trap go horizontal? Apr 15, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Horizontal Merging of Vents & Other Questions Oct 16, 2012
Plumbing Forum, Professional & DIY Advice, Tips & Totally Horizontal T in venting - not as easy as it look. May 14, 2012

Share This Page