High water pressure

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by lennyk, Jan 31, 2010.

  1. lennyk

    lennyk New Member

    Messages:
    11
    Location:
    Port-of-Spain
    Hello,

    I have a house in a neighbourhood with very high water pressure 100+psi.
    A pressure reducing valve was installed and appears to work once there is water flowing,
    this was tested at various settings and looking at the gauge.

    However when there is no water used in the house/flowing, the pressure rises to the 100+psi.
    Are PRV valves supposed to work like this or is there a problem with this valve ?

    Thanks,

    L
  2. cacher_chick

    cacher_chick Test, Don't Guess!

    Messages:
    3,244
    Location:
    Land of Cheese
    The PRV limits pressure coming into the house. If the pressure is building from the water heater, the PRV is not at fault. Do you have a working expansion tank?
  3. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,888
    Location:
    New England
    WIth a PRV, you need a working expansion tank so the WH operation which causes the water to expand when it works, has someplace to go. If that isn't the reason for the pressure rising, then the PRV is defective and needs to be replaced or rebuilt. It could be letting pressure rise because of a bad internal seal, dirt, or other defect.
  4. lennyk

    lennyk New Member

    Messages:
    11
    Location:
    Port-of-Spain
    yes, there is no expansion tank, should I just have one installed nearest to the cold input of the water heater ?
    Also are expansion tanks the same as water pump pressure tanks ?
  5. lennyk

    lennyk New Member

    Messages:
    11
    Location:
    Port-of-Spain
    I ran some tests tonight with a pressure gauge, both with the water heater on and off.
    The heater is not the problem as the pressure creeped up to max on the gauge.
    Good thing is that the mains is split into two -
    one for a tank supply which feeds a pump in case water mains supply is off
    and secondly into the house via the PRV.
    I removed the PRV and shut off that supply, I think I am going to leave it that way and have one less
    thing to go bad and just run the house off the pump supply and let the float valves in the tanks take the high pressure instead.
Similar Threads: High water
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & Very hard water, iron, manganese, sulfates and high TDS ADVICE WANTED Jul 4, 2014
Plumbing Forum, Professional & DIY Advice, Tips & How high can a washing machine pump water "uphill"? Jun 7, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Water pressure high? Need PRV. Feb 15, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Higher temperature water heater overflow valve? Jan 30, 2013
Plumbing Forum, Professional & DIY Advice, Tips & Gravity Fed Garden Hose - How High Should The Water Tower Be? Jun 13, 2011

Share This Page