    Quick question - the electrician that installed 200 amp service to my horse barn has a grounding rod laying in the ground horizontally.

    It is a 4' rod buried about 30" down and about 2 feet off the outside wall of the barn...laying horizontally (not driven into the ground).

    Do I need to correct this???? (only came across this when I was installing insulation around the perimeter of the barn 24" underground).
     
  2. ActionDave

    ActionDave Electrician

    Joined:
    Feb 4, 2009
    Occupation:
    Electrician
    Location:
    Colorado
    Ground rods are allowed to lay in a ditch at least 30" deep. They are supposed to be eight feet long.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. DonL

    DonL Jack of all trades Master of one

    Joined:
    Mar 30, 2011
    Occupation:
    Rocket Scientist
    Location:
    Houston, TX
    You could always drive a additional 8 foot rod. Or measure the resistance to see if it meets NEC requirements.

    The electrician should have known, and it should have been inspected.

    1 4 foot rod does seem rather short, but is better than nothing.
     
  5. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina
    Yes this needs to be addressed. I will say that the person that did this is not an electrician but instead an installer.

    The requirement if for no less than two 8 feet rods no less than six feet apart driven straight down.

    First an attempt must be made to install the rods straight down and if this cannot be accomplished then they can lean no more than 45 degrees. If this to fails then direct burial is allowed at a depth of no less than 30 inches but the 6 feet spacing must be maintained.
     
Similar Threads: Grounding Main
Forum Title Date
Electrical Forum discussion & Blog Water pipe grounding Aug 13, 2015
Electrical Forum discussion & Blog No grounding wire... Jun 22, 2015
Electrical Forum discussion & Blog Grounding Whirlpool Tub Feb 5, 2015
Electrical Forum discussion & Blog Grounding in ceiling light. Nov 23, 2014
Electrical Forum discussion & Blog Using grounding bar inside 3-gang metal outlet box Mar 14, 2014

Share This Page