Grounding for Water Heater

Discussion in 'Water Heater Forum, Tanks' started by bob_cville, May 30, 2013.

  1. bob_cville

    bob_cville New Member

    Messages:
    9
    Location:
    Virginia
    Greetings All,

    I'm replacing a failed electric water heater that was connected with 10-2 romex wire without ground. The inspector says that since it was that way before it is grandfathered in but it seems to me that it would be safer if it was grounded. Immediately above the water heater there is a large (#6 or #8) solid wire clamped to the cold water pipe which runs back to the grounding bar on the main panel. Is it a good idea to connect a wire from the ground screw on the water heater to the clamp on the water pipe? If so what gauge wire? If not, what should I do? Just be happy that the inspector said it was grandfathered? Run a new 10-2 with ground all the way back to the panel?

    Thanks in advance for advice on this.

    -Bob
  2. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,642
    Location:
    Cave Creek, Arizona
    ground

    Ideally, that ground should NEVER conduct any electricity, but to be safe a #10 or # 12 ground wire will be sufficient connected to the existing ground clamp.