Grounding after changing to plastic service line

Users who are viewing this thread

Smith333

Member
Messages
136
Reaction score
4
Points
18
Location
Wisconsin
My #4AWG main grounding wire terminates with a clamp on my galvanized service pipe just before it leaves the house and goes out to the well, which is about 15 feet outside the house. The house plumbing is all copper. If I replace the galvanized service line with polyethylene, could I extend the #4 ground wire outside and clamp it to the steel well casing, and forgo driving two ground rods into very rocky soil? If this is allowable, is there a specific clamp designed for such a purpose?
 
Last edited by a moderator:

Smith333

Member
Messages
136
Reaction score
4
Points
18
Location
Wisconsin
Isn't a well casing like a giant ground rod? This is what the termination looks like. It'll be a few months before I start this project. Thanks

kat-d-01.jpg
 
Last edited by a moderator:

Drick

In the Trades
Messages
460
Reaction score
19
Points
18
A well casing is far superior than a ground rod for grounding. That said its not to code to use it for that purpose (go figure). Driving the ground rods may not go as badly as you think. I've driven them in some very rocky situations and they still go in about 80% of the time. Keep a pair of vice grips handy. They are useful in freeing up rods that only make it in part of the way. Move over two feet and try again if this happens. Nothing says they have to go straight down - you can drive them at a bit of an angle if you need to.

FYI you are supposed to ground the well casing. Where I am no one does it, but to do it all you have to do is drill a hole near the top of the casing, attach a lug using a bolt for the correct gauge wire you are using, and connect it to the ground wire that should have already been run from the panel to the pump - that is assuming your pump even has a ground wire. Also, feel free to run a piece of #4 from your panel to the well head and say it is there to ground the well casing as this will meet code (again, go figure). However, you will still have to drive the ground rods as you can't claim the well as your grounding electrode, even if it is.

rick
 
Last edited:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
In the Seattle area, anytime we do a repipe that removes metal pipe and changes to non-ferrous piping, we're required to use two grounding rods.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Rent a 30lb jack hammer. In very rocky soil it may take even an hour with a jack hammer, per rod. But it always works for me. It can be quite exhausting, to be up a ladder with a heavy tool that vibrates viciously, and is only driving the blasted rod 1/16" per minute, demanding that you lean on the wretched thing. But it will do the trick.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
Oh, and why are you replacing the galvanized with plastic?

Why not use copper? The thicker stuff?

You are going to dig anyway. You say it is only 15'. That is not a lot of material.

Hell, 15' of copper pipe 18" below grade will create quite a lot of ground. Not enough for code, I bet, but not nothing.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
What do you mean by this?
A copper pipe in contact with soil for 10' or more is a perfectly acceptable grounding electrode.

Lying horizontally? As the only ground?

My understanding was that one ground element needed to go DOWN.

Certainly that is what inspectors around here expect. I'm in a desert, mind you.

The copper pipe bringing in the water supply is an excellent supplemental ground. But my inspectors want a ground spike.

Way out in the driest deserts of CA I understand that large metal plates are laid down in the ground a few feet below grade, just because there is so little moisture. But that is not the way we do things here.

But if you want to tell JAR that 15' of copper pipe is enough, then I defer to you. Certainly I would be completely comfortable if it was bonded to his metal well.

drick is pretty emphatic that the well casing is not a valid ground, per code. I don't know what the local authorities want, but if JAR gets lucky, he gets to claim the 15' of copper as one of two grounds, and needs to drive only one rod.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
There is no such requirement than one electrode needs to go "down". Someone in your area made this up.

An inspector can want all he wants, but code is code. A metallic water pipe, in contact with soil for 10' or more, MUST be used as an electrode if it exists, and is considered the primary electrode. This must also be supplemented by another electrode, typically a rod (or two). Even these supplemental electrodes must meet the 25ohm requirement, although very few inspectors enforce this.

I don't care where you are, a 10' long copper pipe is a much better electrode than an 8'x5/8" rod. Not that they do very much at all anyway.
 
Messages
594
Reaction score
0
Points
16
Location
Los Angeles, CA USA
OK, so the code demands two grounds, one of which must be the water supply assuming one exists.

Great. Dig a trench for the second one rather than driving a rod if you prefer.

I can only tell you that I have never had this discussion with any inspectors in my region who did not insist on a ground rod.

Feel free to come out and tell them that they are wrong. Lucky thing for me is that most of the region is sand, and the rods can be driven by hand, at least half way.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
OK, so the code demands two grounds, one of which must be the water supply assuming one exists.
I never said that. I said if a water pipe exists then it must be used, along with supplemental electrode(s).
Code requires ONE electrode minimum. If you have a Ufer (concrete encased electrode), with non metallic water entry, then that is ALL you need. Nothing more.



Great. Dig a trench for the second one rather than driving a rod if you prefer.
Who ever said this? You can lay it in a trench only if driving is not possible.



I can only tell you that I have never had this discussion with any inspectors in my region who did not insist on a ground rod.
Do you only go by what you are told, or do you know what is right before hand?



Feel free to come out and tell them that they are wrong.
I wouldn't initially. I'd politely ask them where it is in the code. If they cannot produce a valid code citation THEN I'd tell them they are wrong. Inspector cannot simply ask for sh*t they want done. They are there to interpret and enforce the code, NOT make it up.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
I never said that. I said if a water pipe exists then it must be used, along with supplemental electrode(s).
Code requires ONE electrode minimum. If you have a Ufer (concrete encased electrode), with non metallic water entry, then that is ALL you need. Nothing more.



Who ever said this? You can lay it in a trench only if driving is not possible.



Do you only go by what you are told, or do you know what is right before hand?



I wouldn't initially. I'd politely ask them where it is in the code. If they cannot produce a valid code citation THEN I'd tell them they are wrong. Inspector cannot simply ask for sh*t they want done. They are there to interpret and enforce the code, NOT make it up.



Did someone piss in your Wheaties ?
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
I have never heard of the UFER being used a a "ground rod". Basically, every building has a UFER, but every building also has a ground rod, or two, or a metallic water service line. In fact, here, when the building has a PVC service line, the breaker panel HAS to have a "Non-metallic water supply line" warning on its face.
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
I have never heard of the UFER being used a a "ground rod". Basically, every building has a UFER, but every building also has a ground rod, or two, or a metallic water service line.
Well, a Ufer is a grounding electrode, not a ground rod.
Like I said, even with a non-metallic water entrance, with a Ufer NO other electrodes are required or needed.

It's all in the code.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Well, a Ufer is a grounding electrode, not a ground rod.
Like I said, even with a non-metallic water entrance, with a Ufer NO other electrodes are required or needed.

It's all in the code.

I ground rod is a electrode, but a electrode is not necessarily a ground rod.

I got the picture.

Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe.

And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not.
 

Chris DeLong

New Member
Messages
2
Reaction score
0
Points
0
Location
New Jersey
Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe.

And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not.

Why would a warning on the gas meter be required?

The grounding electrode conductor must terminate in accordance with (1), (2), or (3).

(1) Buildings or Structures With an Intersystem Bonding Termination. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the intersystem bonding terminal [Art. 100 and 250.94], as shown in Fig. 1. Bonding all systems to the intersystem bonding termination helps reduce induced potential (voltage) differences between the power and the radio and television systems during lightning events.

(2) In Buildings or Structures Without Intersystem Bonding Termination. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the nearest accessible location on the following:

• Building or structure grounding electrode system [250.50].

• Interior metal water piping system, within 5 ft from its point of entrance [250.52(A)(1)].

• Accessible means external to the building, as covered in 250.94.

• Metallic service raceway.

• Service equipment enclosure.

• Grounding electrode conductor or the grounding electrode conductor metal enclosure.

(3) In Buildings or Structures Without a Grounding Means. The grounding conductor for the antenna mast and antenna discharge unit must terminate to the nearest accessible location on the following:

• Any individual electrodes described in 250.52

• Structural steel grounded in accordance with 250.52(A)(2)
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Quote Originally Posted by DonL "Around here I have seen Dish installers that connect to any Metal pipe available, Including Gas Pipe. And the gas lines are plastic feeding the houses. There should be a warning on the gas meters but there is not."

Why would a warning on the gas meter be required?


Because Many People do not follow code and have know clue what you are talking about.
 
Top