Ground wire size

Discussion in 'Electrical Forum discussion & Blog' started by Giles, Feb 7, 2011.

  1. Giles

    Giles Retired tool & Die and Mechanic

    Joined:
    Aug 28, 2007
    Occupation:
    Retired
    Location:
    N.W. Alabama--Florence--
    Over the years, I have noticed that on some romex type wire and some extension cords have a ground wire that is smaller then the load wires.
    I always thought it was correct to have the same gauge wires.
    When is a smaller ground wire ok?
     
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    The ground wire is there for safety...not for normal current flow. Current flow is designed to go from the hot to the neutral. If, for some reason, there is a fault, the ground provides a path that is sufficient to blow the fuse or trip the CB...therefore, any current in the ground is only there a very short time, so it shouldn't heat up like a larger wire could, and is sufficient. For this reason, you can save some money by using a smaller wire there, and most places do.
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. cacher_chick

    cacher_chick Test, Don't Guess!

    Joined:
    Jan 5, 2008
    Occupation:
    Test, Don't Guess!
    Location:
    Land of Cheese
    An equipment grounding conductor is sized based on the over-current protection installed on the circuit. 15A circuit=14ga, 20A=12 ga, 30-60A=10ga, 70-100A= 8ga, 110-200A= 6ga. The grounding conductor may be larger than this minimum requirement, but should not be smaller.
     
  5. TWEAK

    TWEAK New Member

    Joined:
    May 17, 2009
    Location:
    Bay Area CA
    NEC and most all local codes allow a smaller equipment ground for most general circuits. IIRC, there are some exceptions in the NEC where you can't do this. But for the most part it's allowed and perfectly safe. Most current Romex I get (southwire) has the same size ground as the conductors, though - but I've torn out a lot that had a smaller equipment ground. When running THHN/THWN I always take advantage of the code and run smaller ground... with the cost of copper it really saves money, and is perfectly safe. There's no reason I can see for ever running an equipment ground that's larger than the current carrying conductors.
     
  6. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Joined:
    Jun 16, 2007
    Occupation:
    Licensed Electrical Contractor
    Location:
    NY State, USA
    The question was WHEN was the reduced ground NM cable used or allowed. I for one do not know for sure, but it was definitely popular in the 50's and 60's. I think once they realized that a #16 ground was not adequate for a 20A or 30A circuit that is when they went to full size grounds for #14 thru #10 cables.
    Most likely early 70's?
     
  7. jwelectric

    jwelectric Electrical Contractor/Instructor

    Joined:
    Jun 14, 2007
    Occupation:
    Instructor
    Location:
    North Carolina
    The 1962 cycle in Section 250-95 a 20 amp circuit was the lowest listed with a number 16 as the equipment grounding conductor. By the 1968 cycle a 15 amp overcurrent device required a 14 for equipment grounding
     
Similar Threads: Ground wire
Forum Title Date
Electrical Forum discussion & Blog Ground Wire May 20, 2015
Electrical Forum discussion & Blog Can ground wire contact insulation? Feb 9, 2015
Electrical Forum discussion & Blog Adding Ground Wire to Kitchen Stove Jan 19, 2015
Electrical Forum discussion & Blog Ground Wire to Water Pipe Oct 17, 2014
Electrical Forum discussion & Blog 50A 240vac circuit wire and ground in conduit May 22, 2014

Share This Page