GFCI in bedrooms per 2009 NEC?

Discussion in 'Electrical Forum discussion & Blog' started by Thurman, Feb 19, 2009.

  1. Thurman

    Thurman New Member

    Messages:
    9
    During a conversation with two (2) local, licensed residential electricians and one of the local electrical inspectors, on a job site the other day> Any new residential construction after Jan.01, 2009 requires that all 120v circuits within a bedroom be GFCI protected on either a 15 amp or 20 amp circuit, and all 120v circuits within any one bedroom may not be on one circuit. They stated that this was to bring Georgia up to par with the NEC. These electricians and the inspector say this is overkill. You're opinions? Thanks, David
  2. Speedy Petey

    Speedy Petey Licensed Electrical Contractor

    Messages:
    996
    Location:
    NY State, USA
    A) There is NO 2009 NEC. It is the 2008 NEC.

    B) They are talking about AFCI, not GFIC protection.

    I have no idea where Geprgia is on this. Many locations around the country have adopted the 2008 NEC, but have placed amendments on the AFCI requirements.

    Only someone who knows the actual codes in your particular area will be able to tell you.


    I have no idea what this means.
  3. Scuba_Dave

    Scuba_Dave Extreme DIY Homeowner

    Messages:
    885
    Location:
    South of Boston, MA
    Georgia accepted it as of Jan 1st 2009 according to this
    But as said you need to find out if it was accepted in full

    http://www.childoutletsafety.org/files/NECAdoptionMap.pdf

    Also Tamper proof required everywhere (pretty sure)
    Outside must be tamper proof, weather resistant & GFCI

    I think those are the changes - we've been on int since Jan 1st 2008
    I just returned $52+ of 20a PRO heavy duty outlets I can't use
    And they don't have any 20a PRO tamper proof :mad:
    Plus the price is double now
  4. codeone

    codeone Code Enforcement

    Messages:
    160
    Location:
    North Carolina
    NEC 2009 AFCI

    210.12 Are-Fault Circuit-Interrupter Protection.
    (AFCI)
    (B) Dwelling Units: All 125-volt, single-phase,
    15- and 20- ampere branch circuits supplying
    outlets installed in dwelling unit family rooms,
    dining rooms, living rooms, parlors, libraries,
    dens, bedrooms, sunrooms, recreation rooms,
    closets, hallways, or similar rooms or areas
    shall be protected by a listed arc-fault circuit
    interrupter, combination-type, installed to
    provide protection of the branch circuit.


    NC addopted the 2008 NEC last year Mandatory Starting JULY 3 2008
    with some exceptions. This section was delayed until JAN 1 2009
  5. Thurman

    Thurman New Member

    Messages:
    9
    Maybe a little more info and clarification as to what this was all about: It is a State of Georgia Amendment to the 2008 NEC, and is about arc-fault and not GFCI. The link I found is very long but it falls under Georgia's Amendments: "210.12 Arc-Fault Circuit-Interrupter Protection." From what I found it still doesn't explain them talking about not having all duplex outlets in one bedroom on a single circuit, although having the outlets in one room divided up on different circuits is the way I was taught to wire a room so if one circuit fails, you have another for lighting, etc. It seems to be that with any new ruling or amendment to a ruling it takes time for interpretation. I'm still learning every day about something. Thanks, David
  6. Chrissimms

    Chrissimms Master Electrician

    Messages:
    3
    Location:
    Cohutta GA
    Georgia has had arc fault breaker requirements in bedrooms only for several years now. As of 1/1/09 GA has adopted the tamper resistant receptacles in most counties.
    Chris
  7. jbfan74

    jbfan74 Electrical Contractor

    Messages:
    131
    Location:
    Newnan, GA
Similar Threads: GFCI bedrooms
Forum Title Date
Electrical Forum discussion & Blog Do GFCI Outlets Need a Ground? Nov 14, 2014
Electrical Forum discussion & Blog GFCI wiring Jun 2, 2014
Electrical Forum discussion & Blog Hard wired 220v GFCI Questions Jun 2, 2014
Electrical Forum discussion & Blog GFCI receptacle questions May 16, 2014
Electrical Forum discussion & Blog 3-way switching, outside damp location, off of a GFCI Dec 5, 2013

Share This Page