gfci - can i feed multiple receptacles?
Discussion in 'Electrical Forum discussion & Blog' started by bmcleod65, Sep 1, 2008.
  1. bmcleod65
    bmcleod65 New Member
    Jun 22, 2008
    so cal
    I've got a GFCI in the bathroom, middle of a run (two receptacles daisy chained after).
    I want to add another receptacle in the bathroom, can I have the hot run coming into the Line terminal of the gfci and then have two runs coming out of the load terminals (there are two sets of lines and two sets of load holes).
  2. Bob NH
    Bob NH In the Trades
    Oct 20, 2005
    New Hampshire
    Yes. There are limitations in the code regarding where you can put more receptacles on the dedicated bathroom circuit, but there are no limitations on additional outlets in the same bathroom.
  4. Chris75
    Chris75 Electrician
    Aug 12, 2007
    Electrician
    Litchfield, CT
    as long as you dont leave the bathroom your good to go.
  5. bmcleod65
    Jun 22, 2008
    so cal
    Actually the bathroom receptacle I am replacing is in the middle of an existing loop - it then continues off into the bedroom receptacles - should I pigtail the wires so that the bedroom is not on the gfci circuit?
  6. Bob NH
    Oct 20, 2005
    New Hampshire
    You are caught between a rock and a hard place.
    The bathroom circuit may have been installed before the code requirement that other circuits could not be connected to a bathroom circuit. I don't have old codes to check.
    If you install a new bedroom circuit now you would fall under the code requirement that circuits be protected with an AFCI breaker.
    If the work was originally done to code then it is not required to change it.
  7. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    Unless you alter the old installation in which case then........
Similar Threads: gfci feed
Electrical Forum discussion & Blog GFCI tripping with no load when connected to power Oct 7, 2016
Electrical Forum discussion & Blog GFCI shared neutral Aug 8, 2016
Electrical Forum discussion & Blog GFCI replaced, now regular outlet is dead Feb 14, 2016
Electrical Forum discussion & Blog Bathroom outlets tripping garage GFCI Nov 15, 2015
Electrical Forum discussion & Blog Cutler GFCI May 29, 2015