Georgia, 2006 IPC - does this old work look up to code?

Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by dabensys, Sep 3, 2009.

  1. dabensys

    dabensys New Member

    Messages:
    36
    See photo. Note, the WC vents through the 2" VTR noted in the photo.

    Attached Files:

  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    you have a flat vent on the shower that is a no go and the drop down piping on the shower creates an s trap situation which is also a no go.
  3. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Messages:
    1,143
    Location:
    South*East
    Besides the problem NHmaster stated. There are to many fittings. Some one should take an ax to it. I think it's still growing.
    John
  4. FloridaOrange

    FloridaOrange Plumbing Designer

    Messages:
    1,317
    Location:
    SW Florida
    Due to the incorrect venting at the shower the toilet is not vented now.
  5. dabensys

    dabensys New Member

    Messages:
    36
    Thanks for the confirmation. I truly believe that the plumbing work o. This house is bad throughout.
  6. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,650
    Location:
    Cave Creek, Arizona
    Dwv

    There is NO "S" trap. the vent is off the upper level after the trap so it is proper, except for that portion of the shower vent which is horizontal, unless the sink connects to it. There were probably ways to do it more directly without all those fittings, but that is a problem with the installer's experience. For example, the shower could have connected directly to the 3" in the same bay and would not have required the second hole in the joist, and the toilet pipe did not need that "dog leg" in it.