stoneweed1
- Messages
- 6
- Reaction score
- 0
- Points
- 0
I have natural gas entering the house at 1/4 lb pressure. I am concerned about the size of the 1/2" yellow flex csst line to my grill which requires 91000 btus when all burners are lit.
The run to my grill is as follows:
1.5" black pipe runs 40 feet then reduces to
1.25" black pipe that runs 17 feet then reduces to
1" black pipe that runs 11 feet to a tee and continues, but at the tee a
3/4" yellow csst flex trac pipe runs inside 20 feet to the outside where it changes to
1/2" yellow csst flex trac pipe and runs 20 feet in conduit underground to a tee and off of the tee is a
1/2" 12 foot flexible quick connect to the grill
The 1/2" line was there before the grill purchase and there are other appliances that feed off of the black pipe run, however let's just assume that the grill is the only appliance being used when it's lit.
The trac pipe chart states that a 6" - 7" WC pressure with 0.5" drop will give me approximately 70000 btus @ 20 feet of 1/2" trac pipe and 58000 btus at 35 feet of trac pipe. A 12 foot 1/2" tracpipe quick disconnect probably gives about 99000 btus at its best.
I used a digital manometer at the far burner grill orifice and found the pressure to be 6.20" water column with that one burner opened but not lit.
With all
burners open but not lit, the pressure dropped to 5.2" water column. I then turned on the kitchen oven (which is rated at 145000 btus) on high and turned opened a shower and a faucet to hot that sources from a tankless hot water heater (noritz 250,000 btus). And the pressure dropped to 4.25" water column.
The grill specs states 4" water column. The grill does get hot but it takes a good 25-30+ minutes and longer in colder weather. The tech says it should only take 15 min max. The grill's flame looks good with height with one burner lit. With all burners lit on the grill I noticed a very slight reduction in height. At the very least, one burner (25000 btu) is at least adequately supplied.
Questions I have:
I used the tracpipe chart for 0.5" drop. Is that the correct chart to use? The other charts give larger btu ratings
If the digital manometer is showing at least 4" water column pressure at the grill orifice (burner) with and without other appliances lit, am I then getting the max input to the grill that a 1/2" csst trac pipe will supply? Or is the chart at the proper length the btu supply to use?
Am I undersized in using the gas supply 1/2" csst?
If the 1/2" underground csst is undersized (which seems to be the case), would changing the 3/4" csst run inside the house to a 1" csst or black pipe and leaving the 1/2" underground csst make a difference?
If I do have to repipe, would it be just the underground 1/2" or also the 3/4" csst run inside?
I want to keep the grill but would hate to lift up the pavers on this patio to recipe.
A licensed plumber ran the yellow pipe during the patio install and stated ' this pipe should give you plenty of gas', however I'd greatly appreciate advice/opinions. Thanks in advance.
With all
Questions I have: