fuses

Discussion in 'Electrical Forum discussion & Blog' started by jimbo, Aug 1, 2011.

  1. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Can you use a "reject" type fuse such as FRN-R-100 to replace an older ECO brand which did not have the reject notch?
  2. Furd

    Furd Engineer

    Messages:
    446
    Location:
    Wet side of Washington State
    Yes. The 'rejection " (not reject) feature is built into the fuseholder and is to prevent using a lower voltage rated fuse.