    I have installed a Utilitech fluorescent fixture (with two 38w tubes) into my garage ceiling. And I'm using an existing motion detector switch.
    This new light glows when in the motion detect mode (the old one did not) yet it works fine, coming on full when motion is detected.
    Is there a safety issue here? Will this 'glow' cause my ballast to go out sooner?
    Why did the old one not glow, yet the new one does? The new one seems to be a newer energy saving model.

    I'm mostly concerned with safety and life of fixture. Thanks.
  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Bad things are about to happen.

    Fluorescent bulbs are not compatible with many simple control devices like motion sensors and photocells.

    If you want motion control, you need to buy a more sophisticated vacancy or occupancy sensor switch which specifically is says compatible with fluorescent bulbs.
  3. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,153
    Location:
    New England
    Many motion sensors remain powered by being inline with the load and expect the load to be something like a lightbulb. Yours apparantly does and is seeing the ballast transformer as a load and running current through it to power itself. There are some that do not connect and use the load to complete the circuit, and use a relay to power the load when motion is sensed. this can be done with SS, but it must be designed for it and generally, would require access to both the hot AND neutral to function.
  4. MoMan

    MoMan New Member

    Messages:
    2
    Location:
    Southeast Texas


    "Bad things?" Like what? The motion sensor is working even if it is not as it is supposed to be.
    Please address the safety and ballast question. Thank you.
    MoMan
  5. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    I can't say if "safety" i.e. fire is an issue. But you will experience short bulb life, possibly short ballast life.
    When a manufacturer says "don't do it" they usually have good reason for that.
  6. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,153
    Location:
    New England
    If the motion sensor isn't using something like a relay to turn the lamps on/off, it is constantly supplying a small voltage to the ballast so that it can power itself, IOW, it's in series with the load and the load is completing the circuit...no complete circuit, no power to make the motion sensor work. That's why I said a better choice for this is a motion sensor that has an available neutral so it doesn't need the load to complete the circuit. When the load is not getting the full voltage and has constant low voltage being applied, it can result is short life, increased heat, and potentially a fire. Also, some motion sensors, even when they are tripped, without a relay, act like an in-line load, which reduces the voltage to the device. Now, they are designed, when on, to minimize their internal voltage drop, but it's never a true short like an on/off switch is. A relay acts as an on/off switch. Unless the fixture and the motion sensor are designed to work together, short life and extra heat and problems can occur.
Similar Threads: Flourescent Light
Forum Title Date
Electrical Forum discussion & Blog flourescent lights won't work together Aug 12, 2009
Electrical Forum discussion & Blog Static interference from flourescent lights. Mar 19, 2009
Electrical Forum discussion & Blog Replacing Flourescent Ballast Dec 1, 2008
Electrical Forum discussion & Blog flourescent ballast ??? May 11, 2008
Electrical Forum discussion & Blog Compact flourescent bulbs Mar 13, 2008

Share This Page