expansion tank

Users who are viewing this thread

ddenney

New Member
Messages
8
Reaction score
0
Points
0
can anyone tell me the location an expansion tank should be installed in regard to a water heater? Also should the tank hang below the water line or be above it?
 

Gary Swart

In the Trades
Messages
8,101
Reaction score
84
Points
48
Location
Yakima, WA
It can be anywhere in the supply line after the PRV, but the usual place is between the water heater and the PRV. The exact orientation of the tank is not important, but it must be supported. I think the best way is to install it so that it hangs below the pipe. That way the pipes can be strapped to a floor joist on both sides of the tank and provide excellent support. However, sometimes the physical location of the pipes make that difficult or impossible, and then other means of support must be provided. There are several suggestions on the Watts box.
 