    OK. Boxes have max capacity fill, conduit, etc.

    What about MC/AC wire. Is the *clad* good enough on how much *capacity* the wire inside needs.


    I plan to put a 4" square box on a wall that has been mudded/rocked over.
    It's roughly 1 1/4"+ in depth so to make this fairly seamless, I plan to channel out the wall, run the BX in the channel and then plaster the BX in place. I plan to take a chipping hammer and chip out the area where the box will be so it sits flush with the wall (poured concrete wall).

    Is is ~okay~ to bury the wire in plaster ?
    Or does it need room/air around it.
  2. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,615
    Location:
    Cave Creek, Arizona
    If you do not overload it, it should NOT overheat or need ventilation other than what flows through the armored covering.
  3. michielsemma

    michielsemma New Member

    Messages:
    6
    Location:
    Utah
    Breaker needs to be a 40 amp and wire needs to be 8 AWG. A 30 amp breaker will nuisance trip on hard starts. Full load amps is when it's running at full capacity. Starting current is a lot higher than FLA.

    Check to see what size the main wires are on the unit where you are supposed to make your connection from the breaker panel. If the wires are bigger than 10awg or add up to be bigger than 10awg then you cannot use a 30 amp breaker.

    Look for a rating of minimum circuit ampacity on the unit as well.

    Your fuses or breakers are designed to protect the wiring in your home from short circuits and overheating and starting a fire. They are not designed to protect your appliances. You cannot legally run a 10awg wire to a 50 amp breaker.
  4. Jerome2877

    Jerome2877 In the Trades

    Messages:
    397
    Location:
    BC
  5. BobL43

    BobL43 DIY Senior Member

    Messages:
    1,792
    Location:
    Long Island, NY
    And what does that have to do with ChefWong's question anyway? he never mentioned the load as far as I can see.:rolleyes:

    As jerome said, just a copy and paste job from you
Similar Threads: Electrical Wiring
Forum Title Date
Remodel Forum & Blog 2 electrical question re: deck renovation Aug 22, 2011
Remodel Forum & Blog Gutted living room - Electrical/Insulation question Jan 29, 2009
Remodel Forum & Blog Rough plumbing / electrical inspections Feb 25, 2007
Remodel Forum & Blog Electrical Work, Dryer Outlet Jun 28, 2006
Remodel Forum & Blog Rewiring setup question. Feb 26, 2009

Share This Page