    I have a couple of question that I'm hoping someone can answer, any response will be greatly appreciated.
    1. It states in the code book that type nm ROMEX® run thru floors is to be protected by conduit for a distance of 6" above the floor. Are they talking about in an open floor outside of the stud wall? I thought ROMEX® inside a stud wall can run unprotected thru the sub floor and bottom plate.

    2. I have a 200 amp panel mounted on the wall of a garage. I cut out a 1/2" plywood board and put it around the panel. My ROMEX® (14-2, 12-2, 10-2 and 3)is coming down from the attic and I plan to fasten it to the plywood. My question is: is this an appropriate method of wiring the runs back to the panel? I guess what I'm concerned about is the unprotected ROMEX® from the ceiling to the panel, but I have seen this on other installation whether correct or not.

    Thanks
    Last edited by a moderator: Dec 7, 2011
  2. jwelectric

    jwelectric Electrical Contractor/Instructor

    Messages:
    2,566
    Location:
    North Carolina
    You will be fine coming through the bottom plate. The Sheetrock will protect it for the first six inches

    It is going to be hard getting the cables into the panel if it is covered from the top of the panel to the ceiling.

    A close read of 110.26 and you will see that from the floor to a height of six feet above the panel or to the ceiling three feet out and 30 inches side to side belongs to the panel and is not to be blocked. This requirement is all the protection that the cables coming into the panel need.
    Last edited by a moderator: Dec 7, 2011
Similar Threads: Electrical Questions
Forum Title Date
Electrical Forum discussion & Blog Random electrical wiring questions May 27, 2013
Electrical Forum discussion & Blog 2 electrical questions Jun 28, 2010
Electrical Forum discussion & Blog Basic electrical questions Aug 30, 2009
Electrical Forum discussion & Blog Water questions for the electrical experts!!! Mar 3, 2009
Electrical Forum discussion & Blog Questions for the Electrical Guru Nov 28, 2008

Share This Page