Electrical Boiler

Users who are viewing this thread

Status
Not open for further replies.

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
2 copper NM-B or 2 SE-R copper is good for 95 amps. As long as the boiler ampacity is below 76 amps then installing it using #2 with a 100 amp breaker will be fine.
If the heating elements are rated at more than 48 amps and the boiler does not have an ASME stamp on it then the maximum ampacity cannot exceed 60 amps. If the boiler does not have an ASME stamp and the elements are rated more than 48 amperes the load has to be divided into loads that does not exceed 60 amps. This can be done inside the control panel of the boiler by having fuses or breakers that subdivide the loads.

Once again please do a service load calculation to be sure that it will handle the new load. Remember that the boiler is to be figured at 125% of its ampacity.

read this .
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Exactly.

Also the manufacture says #2 , It is UL listed, so its got to be correct. Right ?

If the boiler is rated at 24KW then it will require a conductor rated at 125 amps regardless what the installation instructions say.
The more strenuous rule will take presence.

Remember that the NEC is a minimum safety standard so to do anything less than what it calls for leads to an unsafe installation.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
If the boiler is rated at 24KW then it will require a conductor rated at 125 amps regardless what the installation instructions say.
The more strenuous rule will take presence.

Remember that the NEC is a minimum safety standard so to do anything less than what it calls for leads to an unsafe installation.

I Don't really think that it is going to Be using 24KW that is just a selling point that people fall for. Bigger is better ?

The True rating is in BTU, Then when you do the math, their own figures don't add up.

It works just like a water heater, Well it is one, and all Heating elements will not be in operation simultaneously.
 

Nukeman

Nuclear Engineer
Messages
707
Reaction score
1
Points
18
Location
VA
Don,

How do you figure? At 24KW, I get ~81,900 BTU (thermal) per hour, which agrees with the 82,000 BTU/hr listed earlier. Maybe you are looking at a different unit?

Even if it doesn't pull 100A 100% of the time, the wiring needs to be sized for a 100A load (really sized for 125A).

As I (and others) brought up earlier, we don't know that this house even needs a 82k BTU/hr unit. We also don't know anything about the "new house" either. One of the smaller units might get the job done and will cost less for the unit as well as the wiring, breaker, etc.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
I Don't really think that it is going to Be using 24KW that is just a selling point that people fall for. Bigger is better ?

The True rating is in BTU, Then when you do the math, their own figures don't add up.

It works just like a water heater, Well it is one, and all Heating elements will not be in operation simultaneously.

A boiler is different than a water heater. The boiler is designed to allow all the elements come at one time. On the first start up when the water is cold it is possible for all the elements to draw current at the same time.

The NEC requires that the KW rating of the boiler to be multiply by 125% for sizing the conductors. If the name plate on this boiler says 24KW then it is 24,000 times 125% for sizing conductors.
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
You guys are exactly correct.

When you look at the units Controller Sequencing a different story is told.
 

technogirl74

New Member
Messages
19
Reaction score
0
Points
1
Location
New York
Thanks for all the answers guys.

Spent the better part of yeaterday talking to some contractors to instal as well as Slant Fin technical assistance.
The boiler fully running draws 93amps with the circulator included.
The elements are modulated to come on as needed. The boiler has an outdoor reset built in to it.

Originally we were going to try and do alot of this work ourselves but we really liked one of the contractors.

He's proposing to run 2/0 copper SER out of the panel. (On a 100 amp breaker) to the boiler.
When he pipes in the boiler, he''s gonna make it so that we can valve off the electric boiler and switch to the propane boiler and vice versa.

JW. Speedy Petey, DO YOU GUYS SEE ANY ISSUE/PROBLEM WITH USING 2/0 SER ON A 100 AMP BREAKER? (not shouting)
Could we get away with 1/0?
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
You could use 1/0 copper SE type cable and a 125 amp breaker. This is something that your electrician should know and if he don’t you might want to consider another electrician.

For reference have him/her look at 424.72 of the NEC and the sections that it references
 

DonL

Jack of all trades Master of one
Messages
5,205
Reaction score
72
Points
48
Location
Houston, TX
Thanks for all the answers guys.

Spent the better part of yeaterday talking to some contractors to instal as well as Slant Fin technical assistance.
The boiler fully running draws 93amps with the circulator included.
The elements are modulated to come on as needed. The boiler has an outdoor reset built in to it.

Originally we were going to try and do alot of this work ourselves but we really liked one of the contractors.

He's proposing to run 2/0 copper SER out of the panel. (On a 100 amp breaker) to the boiler.
When he pipes in the boiler, he''s gonna make it so that we can valve off the electric boiler and switch to the propane boiler and vice versa.

JW. Speedy Petey, DO YOU GUYS SEE ANY ISSUE/PROBLEM WITH USING 2/0 SER ON A 100 AMP BREAKER? (not shouting)
Could we get away with 1/0?


It all has to do with Duty Cycle. Go for it. The worst than can happen is the breaker will Need reset often. But not likely if the controller is properly setup.
 
Last edited:

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
The link you posted on the cover of the manual is calls it a boiler

Perhaps its a canadian thing. When you read deeper, it certainly does not make any mention of steam production, but only as use for hydronic heating. Boiling water in Pex would be rather a problem. Maybe the OP will clarify.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Perhaps its a canadian thing. When you read deeper, it certainly does not make any mention of steam production, but only as use for hydronic heating. Boiling water in Pex would be rather a problem. Maybe the OP will clarify.

It does not have to produce steam in order to be a boiler. Most water heaters are ASME rated as a boiler
 

technogirl74

New Member
Messages
19
Reaction score
0
Points
1
Location
New York
JW,

Its actually an HVAC contractor that will be doing the install. Here he is allowed to do the electrical as well.
We discussed permits and I talked to the town and they said that I do not need one. (Yippee)

I priced 2/0 as opposed to 1/0 and for a few additional dollars I will be going with the 2/0.
You mentioned SE cable, the boiler directions call for two hots, a neutral and a ground. Wouldn't that be 4 wires. I was told SE cable is only 3.


Also, do you any issue with the breaker being a 100 amp.
I called and they do not make a 125 amp breaker for my panel.

thanks again.
 

JWelectric

Electrical Contractor/Instructor
Messages
2,608
Reaction score
21
Points
38
Location
North Carolina
Maybe I should have said SE-R which is a 4 conductor cable. In the trade most will know that SE sometimes means SE-R

It is up to you as to what you use. What I have posted is what the NEC requires
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
Perhaps its a canadian thing. When you read deeper, it certainly does not make any mention of steam production, but only as use for hydronic heating. Boiling water in Pex would be rather a problem. Maybe the OP will clarify.

It's not a Canadian thing, it's a hydronic thing (steam also fall under the "hydronic" heading, BTW), and they are indeed boilers, not mere water heaters despite the lack of steam output.

In a pumped liquid hydronic boiler micro-boil bubbles are constantly forming and collapsing along the heat exchanger surfaces, and it's the designed such that the turbulence on the water side sufficiently high to keep the micro-boil bubbles from collecting and become an insulating film. But taht creation and subsequent collapse of the water vapor bubblets is an important part of the heat exchange process- it's designed-for. When there isn't sufficient system pressure (or slow flow) that micro-boil can become large enough to sizzle audibly, and when the bubbles are allowed to get that big the stack temps go up, combustion efficiency falls. (This is an issue with gas-fired tankless HW heaters at low water pressure too. A tankless HW heater is actually a boiler too, and referred to as such in some countries.)

Even on fossil-fired condensing boilers where the flue temps are well below the boiling temp of water, micro-boil is occurring a the end of the HX nearer the flame front, but ceases in the condensing end of the HX.

With modulating electric boilers there may be operating temperature ranges on the low end where they don't actually get the micro boil, but that depends also on flow rate and the modulation power. While related in some ways to their technologically similar on-demand electric HW heaters, they're designed to tolerate a much higher temperature range and flows more relevant to hydronic heating applications. They are uses ALL THE TIME in radiant heating apps in conjunction with PEX tubing, but have to be output temp limited to stay within the operating range of the PEX (most often specified at 180F by the manufacturers, but they're actually good for at least 20F more at typical heating system pressures), and are widely available from a number of manufacturers and internet vendors, eg: http://www.pexsupply.com/pex/control/search?SEARCH_STRING=electric+boilers
 

Ballvalve

General Engineering Contractor
Messages
3,581
Reaction score
45
Points
48
Location
northfork, california
It does not have to produce steam in order to be a boiler. Most water heaters are ASME rated as a boiler

Thats a bit redundant. You answered your own original question. Or was it a test?

They are uses ALL THE TIME in radiant heating apps in conjunction with PEX tubing, but have to be output temp limited to stay within the operating range of the PEX (most often specified at 180F by the manufacturers, but they're actually good for at least 20F more at typical heating system pressures), and are widely available from a number of manufacturers and internet vendors, eg: http://www.pexsupply.com/pex/control/search?SEARCH_STRING=electric+boilers

I have 3000 feet of pex in my slab, and I certainly would stay well UNDER the temp and pressure at all times. Not a good place for a "test" of specifications. In fact, that unit scares me, as if it ever ran away on temperature, you would be calling the HVAC guys in.
 
Last edited:

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
How is an electric boiler's runaway risk different from a gas-fired boiler? Either could runaway in temperature (hell even a hot water heater can) but only if multiple controls have failed. The SlantFins even come with outdoor reset control, if you want it for a higher comfort constant flow setup. If the internal controls scare you, inserting a high-limit aquastat on the output piping to interrupt it may be cheap insurance, but not necessary. They come with the usual 3rd party test ratings for hydronic boilers, including ASME (which isn't often the case for hot-water heaters.)

I'd never design ANY heating system for 180F water, but Wirsbo has a test setup that's been running a length of PEX for over 25 years at elevated temp and pressure beyond the rated spec. An excursion to 200F isn't going to be a disaster with anybody's PEX, but 220F might if the pressure relief fails. Wirsbo rates theirs at 200F @ 80psi, an insane temp & pressure for radiant floor applications. "Brand X" PEX is often only rated at 180F nominal operating temp, but it can take much more at typical heating system pressures.

But I s'pose with an idiot system designer it's possible to defeat about any safety or temperature limit spec. :)

Electric boilers are relatively simple-minded & rugged beasts, and they're cheap. But even in nickel a kilowatt-hour land, in an upstate NY climate the total seasonal energy requirements it won't be ultra-cheap to operate. The boiler in question is likely to be more than 2x oversized for the load too, which is never a good idea for comfort and equipment longevity. Money spent on it is better spent elsewhere:

A 1.5-2.5 ton inverter-drive ductless air source heat pump (mini-split) appropriately sized for the heating load would pay for itself in under 5 heating seasons even with nickel electricity (and that's at the full installed price of the heat pump not some delta between an electric boiler installation and a mini-split.) Going with an electric boiler and NOT a mini-split would only make sense if you were willing to pay for the extra comfort-cush of a radiant floor or something. A heat pump with some cheap resistance electric backup for the sub-zero peak loads makes more sense otherwise. It would have have half (or less) the operating cost of an electric boiler during mid-winter, and less than 1/3 the operating cost during the spring & fall. In a ~7000 heating degree day climate those are significant savings.
 