    I'm rough plumbing a house I'm building and I've gotten stuck on this one wall where two bathrooms meet back to back.
    I'm worried about where the shower and tub wastes meet at that double-fixture tee. Is that okay? Is that an okay way to vent those two fixtures? Is this long main waste line vented properly?
    The toilets are wall-hung in Geberit carriers and that's why the drain is in the wall with the vent following behind it.
    [​IMG]
    Thanks for your time!
  2. Terry
    Aug 17, 2004
    For the toilets you would wye or combo off the main line and vent between that fitting and the fixture.
    The way it's drawn now is wrong.
    The lavs and the tub/shower combo is right.
  4. hello_mundo
    Dec 18, 2008
    Santa Cruz, CA
    Thanks Terry. I was looking at the Geberit Install documentation and they had the vent set up the way I've drawn it. But I think I understand why your way is better. Thanks!
  5. Terry
    Aug 17, 2004
    I imagine they have the vent downstream, and that is how you vent.
    But when you add other fixtures before the vent, it is no longer downstream.
  6. jar546
    jar546 In the Trades
    Feb 20, 2008
    USA
    Don't worry about the double tee for the Tub and Shower. That is not a problem at all. Only be careful when you double tee back to back toilets. In that case, you need to have at lease 18" of horizontal pipeon each side before it hits the tee from both sides.
    Don't forget all of your vertical to horizontal connections must be Wyes and not tees on their back (except for vents).
    I agree with Terry's assessment
  7. hello_mundo
    Dec 18, 2008
    Santa Cruz, CA
    Thanks guys! I really appreciate your time and help. This forum rocks!
  8. nhmaster
    nhmaster Master Plumber
    Jul 30, 2008
    Tech. Instructor
    S. Maine
    The only problem I have with back to back san tees is when it comes time to run a snake down the drain it usually scoots across to the other fixture.
  9. hj
    Really?
    quote; Only be careful when you double tee back to back toilets. In that case, you need to have at lease 18" of horizontal pipeon each side before it hits the tee from both sides.
    1. WE cannot use a double tee/cross for back to back fixtures of ANY kind.
    2. 18'' of horizontal pipe each way, plus a "cross", would give you at least an 18" toilet roughin on both sides more if you are not counting the elbow.
  10. SewerRatz
    SewerRatz Illinois Licensed Plumber
    Nov 20, 2008
    Chicago Illinois Licensed Plumber
    Chicago, IL
    Thats why You put a wye combo on the vent and run the pipe to the nearest wall with a plug so you have a clean out on the drop.
  11. theplumber
    theplumber Member
    Dec 20, 2008
    CA
    The only issue I have is the sizing of the wasteline for the w/c's. I could have sworn you could only keep to 3" if the toilets were at least 16' apart. Otherwise you have to go to 4" after the drop from the toilet closest to the sewer if they are closer than that.
    It may depend on local codes, I'm not sure if that's just an L.A. thing or if I'm completely mistaken.
  12. jar546
    Feb 20, 2008
    USA
    Exception: Back-to-back water closet connections to double
    sanitary tees shall be permitted where the horizontal
    developed length between the outlet of the water closet and
    the connection to the double sanitary tee pattern is 18 inches
    (457 mm) or greater.
    I don't agree with it but it is allowed.
  13. hello_mundo
    Dec 18, 2008
    Santa Cruz, CA
    Quote: I could have sworn you could only keep to 3" if the toilets were at least 16' apart.
    I'm not positive, but I designed it this way because the code book said that 3" ABS could support 20 fixture units (that's IRC... UPC says 35) on a horizontal branch. A W.C. is 3 fixture units, so that allows lots of room.
Similar Threads: Question
Plumbing Forum, Professional & DIY Advice Bathroom sink remodel venting/drain question Today at 1:36 PM
Plumbing Forum, Professional & DIY Advice 1950 Renovation Questions Tuesday at 10:06 PM
Plumbing Forum, Professional & DIY Advice Bathroom plumbing question Tuesday at 11:20 AM
Plumbing Forum, Professional & DIY Advice Moen Single Handle Pull Down Kitchen Faucet water supply hose question Tuesday at 6:03 AM
Plumbing Forum, Professional & DIY Advice Moving kitchen sink and dishwasher, vent question Sunday at 6:24 AM