Ducane vent termination

Discussion in 'HVAC Heating & Cooling' started by jar546, Sep 15, 2010.

  1. jar546

    jar546 In the Trades

    Joined:
    Feb 20, 2008
    Location:
    USA
    Ducane 90% with the combustion air taken from inside and not piped from the exterior. Does the manufacturer's installation instructions prohibit this installation?
    [​IMG]
     
  2. jar546

    jar546 In the Trades

    Joined:
    Feb 20, 2008
    Location:
    USA
    4' to the window or gas meter would be the answer.

    This does not comply with the manufacturer's requirements or the fuel gas code
     