Double fixture fitting for toilets

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by Wally Pfautz, Jul 5, 2006.

  1. Wally Pfautz

    Wally Pfautz New Member

    Messages:
    34
    Is there a minimum length requirement (UPC) between a double fixture fitting and closet flanges used for back to back toilets. Another thread alluded to this. I need to use a 10" rough-in toilet on one side, which puts the length from centerline of toilet flange to centerline of DFF vent at about 12.5". The other toilet flange dimension is only about 14.5" as well.

    Is this wrong? Thanks,

    Hazel

    P.S. - I posted this on the toilet thread but urgently need the answer so sorry for the duplication.
  2. Mikey

    Mikey Aspiring Old Fart, EE, computer & networking geek

    Messages:
    2,715
    Location:
    Central Florida
    An interesting paper:

    http://www.pmmag.com/CDA/Archives/980678adbcfc7010VgnVCM100000f932a8c0____

    illustrates why

    http://www.psdmagazine.com/pdf/Nov_Dec_04/48_60.pdf

    claims that "With the superior flushing of the 1.6-gpf water closet, the plumbing codes have prohibited the installation of a double sanitary tee or double fixture fitting for back-to-back water closets." They go on, and say that you can use a double combination wye and a 1/8 bend, or a double sanitary tee at least 30 inches from the centerline of the WC outlet. No explicit mention of the DFF, but it looks like the 30" rule mught apply there as well.

    Disclaimer: I don't have access to an honest-to-God Code book, but it probably doesn't matter. What matters is what your local authority wants.
  3. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,797
    Location:
    Cave Creek, Arizona
    fitting

    I have never seen a prohibition to the standard back to back fixture fitting. A sanitary cross, however, is almost always never permitted. The double Y and street 1/8 bends would normally space the toilet openings too far from the wall.

    [​IMG]
    Last edited by a moderator: Mar 5, 2014
  4. jaynote1

    jaynote1 Plumber

    Messages:
    15
    Location:
    southeastern nc
    good call, hj...i consulted my boss on this one, and his reply matched yours almost word for word...........
Similar Threads: Double fixture
Forum Title Date
Plumbing Forum, Professional & DIY Advice Double Fixture cross Usage with an Immediate horizontal turn Jan 23, 2014
Plumbing Forum, Professional & DIY Advice Double fixture fitting - sink next to washing machine standpipe Jan 19, 2014
Plumbing Forum, Professional & DIY Advice 3 inch Double Fixture Fitting with 2 inch reducers? Nov 23, 2013
Plumbing Forum, Professional & DIY Advice Converting to double sink-drain pipe too close to stud for double fixture fitting. Mar 10, 2012
Plumbing Forum, Professional & DIY Advice Back to back bathrooms without a double fixture? May 19, 2010

Share This Page