Does turning off water main cause issues with boiler?

Users who are viewing this thread

Tim Moyer

Member
Messages
64
Reaction score
6
Points
8
Location
NJ
We turned off the water main in a vacant house we own.
Would doing so adversly affect an oil fired boiler than heats the baseboards throughout the home? The boiler is currently flashing an error and I plan to investigater further today when we visit the home.
 

Sylvan

Still learning
Messages
2,766
Reaction score
695
Points
113
Location
New York
NEVER cut off the water supply to a boiler as you cannot depend on a LWCO to be a failsafe device.
 

John Gayewski

In the Trades
Messages
4,364
Reaction score
1,348
Points
113
Location
Iowa
If there's a leak in your hydronic system then the system won't auto fill when your water is off. So you could potentially loose your heat and ruin all of the piping. On the other hand if you leave the water on and there's a leak the water would not stop running until the water is shut off.
 

Sylvan

Still learning
Messages
2,766
Reaction score
695
Points
113
Location
New York
Even on a steam boiler if there is a leak on the condensate return and the LWCO fails you really do not want any boiler dry firing.

The fuel makes no difference, wood, coal, electric, natural gas, oil, propane etc.
 