Does this shower rough in look ok?

Discussion in 'Shower & Bathtub Forum & Blog' started by Jo Deloco, Jan 30, 2013.

  1. Jo Deloco

    Jo Deloco New Member

    Messages:
    1
    Location:
    Texas
    This is pretty straight-forward shower rough I dry fitted pending comments. I'm not sure if the the wet vent going to the lav is acceptable under IRC (NJ) with the 60 degree fitting. I rolled the combo up slightly above the drain centerline which I hope will be inspection. Thanks for your input.

    Attached Files:

  2. Terry

    Terry Administrator Staff Member

    Messages:
    15,302
    Location:
    Bothell, Washington
    The wet vent portion should be 2"
    It looks fine. :)
    Last edited: Jan 31, 2013
  3. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,056
    Location:
    Cave Creek, Arizona
    According to his notations, the "wet vent" IS 2", but to use a 1/6 bend at the base, the branch should rise at a 30 degree angle which means the main line should be below the floor one half the distance of the branch line dimension to the 1/6 bend, and yours does NOT appear to be that deep, but it could be because of the way the picture was taken. If the angle is correct and not "cocked" in the fitting, then the inspector should pass it, unless he goes "by the book" and wants it at a 45 angle.
  4. johnjh2o1

    johnjh2o1 Plumbing Contractor for 49 years

    Messages:
    1,143
    Location:
    South*East
    The vent is being washed by the lav. there is no need for it to rise at a 45.

    John
  5. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,269
    Location:
    New England
    Now that you've done all that cutting, you realize that you cannot reliably dry fit pvc piping? It is nearly impossible to bottom the pipe in a fitting unless you've added the cement (which melts the plastic and then 'welds' it together). So, unless you planned for that loss of 1/4-1/2" or so per joint, everything's going to be positioned wrong. At least the pipe is cheap...and you can reuse the fittings.
Similar Threads: Does shower
Forum Title Date
Shower & Bathtub Forum & Blog Does this shower head need a ground wire? Oct 9, 2014
Shower & Bathtub Forum & Blog Why does drywall work in a Kerdi Shower? Jan 26, 2014
Shower & Bathtub Forum & Blog Does anyone know what brand of shower faucet this is? Sep 29, 2013
Shower & Bathtub Forum & Blog does anyone know this shower valve? Jan 1, 2013
Shower & Bathtub Forum & Blog Kohler Cartridge 73923-aa For Shower Faucet. Does Anyone Know Where I Can Get This? Oct 8, 2012

Share This Page