If your detached building has no metal connection to the main building, water, gas, conduit, etc, it was acceptable to install only un-grounded and grounded conductors with no EGC. In this case you WOULD bond the neutral to the subs enclosure and the enclosure to the grounding electrode system. This would allow the Neutral to carry ground fault current back to the transformer.

Okay, maybe somebody told me wrong several years ago ... but now I need to run wire to a subpanel in an attached workshop at the back of the garage and house, and I understand that to need four (4) wires and no bonding, correct?

It is, however, required as of 2008 NEC to always run an ECG for an outbulding, (which is always a good idea anyway). Then there will be no issue of wheather bonding is required.

I am a DIY handyman working on my own stuff. What is an ECG?

PS: "ECG" just reminded me of a great brain teaser for nurses: Ask a nurse what an EKG is, and he or she will tell you it is an electrocardiogram (sp?). Next ask what an EEG is, and he or she will say it is an electroencephelogram (sp?). Right after that, ask what an EGG is and you will get a blank stare ... then say it is an egg to be eaten for breakfast.
 
Last edited:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
It sure is dry... Agreed on ground/grounding/earth/bonding issues. I admit to being hazy in this area as well, but the haze is slowly lifting. But as long as you've provided the opening, what DOES a ground rod actually do? It looks like different ground rods do different things, as well. Poking around my house, I see a ground road at the base of the pole supporting the transformer; at the main service entrance below the meter; at an outbuilding with a subpanel; and at the dock (with a subpanel). I hope the local crack addicts don't decide that these are all copper.


A ground rod is simply for limiting the voltage imposed by lighting, line surges, or unintentional contact with higher-voltage lines. It has NOTHING to do with the little hole you see in a receptacle.

In a nutshell, hopefully it will prevent surface arcing from higher voltages.

250.32(A).jpg
 
Last edited:

Chris75

Electrician
Messages
607
Reaction score
0
Points
0
Location
Litchfield, CT
Okay, maybe somebody told me wrong several years ago ... but now I need to run wire to a subpanel in an attached workshop at the back of the garage and house, and I understand that to need four (4) wires and no bonding, correct?

Correct


I am a DIY handyman working on my own stuff. What is an ECG?

That was a typo, should have been EGC, Equipment Grounding Conductor.

The wire that connects to a ground rod is a GEC, Grounding Electrode Conductor.

THis is why electricity is not really a DIY type of job, too much basic theory required even for the simplest jobs.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
...no matter how well-planned, code-compliant, and well-built, we can imagine a scenario where the guy holding on to the appliance gets zapped...

I think those who write the electrical and other codes go by history and what has actually happened in the past. Not what might happen in the future.

If there is one rare freak accident, I don't think that would carry much weight as to changing the electrical code. BUT if there are say hundreds of cases each year of people being electrocuted from the same situation, then they do what they can to change the code to prevent these things from happening in the future.

Then there is the probability that a situation will occur. Is it likely that a lot of people will have situations where there are say 4 electrical problems all at once? Or is it more likely that most people who have electrical problems will have just 1 or 2 problems at a time?

Problems being; neutral which is loose and becomes disconnected, ground wire gets cut, hole drilled in wall severing neutral wire only, an appliance which has a hot wire which is touching the metal case, etc.
 

Billy_Bob

In the Trades
Messages
419
Reaction score
0
Points
0
Another situation I forgot to mention is that with large wires, it is common for there to be a smaller ground wire than the current carrying wires...

We all know that breakers are designed to cut off the electricity if the amperage being used exceeds the capacity of the wire size. (If there is too much amperage flowing through a wire, it can become hot and start a fire.)

There can be a situation where the neutral is bonded to the ground in a subpanel. And the ground wire in the main cable going to the subpanel has a smaller diameter wire than the other wires...

Say the neutral on this cable is loose at one end and becomes disconnected. Then the ground wire would carry the load of the neutral, would not be correctly protected by the size breaker installed, and could become hot and start a fire.
 

kencaz

In the Trades
Messages
6
Reaction score
0
Points
0
Location
Northrige, CA
Okay, maybe somebody told me wrong several years ago ... but now I need to run wire to a subpanel in an attached workshop at the back of the garage and house, and I understand that to need four (4) wires and no bonding, correct?

Correct, The Neutral/White (Grounded Conductor), and the EGC/Green (Equipment Grounding Conductor), should ONLY be bonded at the Main Panel.


I am a DIY handyman working on my own stuff. What is an ECG?

Sorry, my bad. I meant EGC [Equipment Grounding Conductor]. The green wire.

KC
 

Alectrician

DIY Senior Member
Messages
688
Reaction score
0
Points
0
i spoke to a licensed electrician who addmitted it makes no sense to him either.

It took me a while to "figure it out" too.

If you lose the neutral, the current will find it's way into/thru water pipes, gas pipe etc.

Of course if this happens at the service, the same thing will happen but they are tring to minimize the risk.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
... electricity is not really a DIY type of job, too much basic theory required even for the simplest jobs.

Yes, and a lot of common sense. My wife told me her fan did not work in a kitchen receptacle, and it sparked when I tried it to check it out. What I ultimately pried out of the box was a stabbed receptacle packed in foam with a neutral wire that had turned black. I have never done anything anywhere near that bad, but I certainly agree that some people should never do any electrical work at all. Or, maybe a license should be required for applying foam ...
 

Attachments

  • hot stab.JPG
    hot stab.JPG
    43.1 KB · Views: 267
Last edited:

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Well, at least they had air infiltration under control. I sometimes wonder if box fill calculation methods will be changed to derate when dealing with foam-filled or otherwise really-sealedup-well boxes.
 

Leejosepho

DIY scratch-pad engineer
Messages
2,483
Reaction score
0
Points
36
Location
200 miles south of Little Rock
Website
www.nonameyet.org
Good find.

Yes, but the author must have been too young to know the entire story. He or she said:

The only reason why the prongs on the two-prong plug are different sizes is to ensure that the more dangerous connection [used for an incandescent lamp], the more accessible threaded socket, is always connected to the neutral, or safer, wire ...†(emphasis added)

The matter of light-socket safety is not the *only* reason for differently-sized prongs. Many years ago, just plugging a floor or table lamp into the wall and reaching for the switch could result in a shock since the ground-ed (neutral) conductor also inadvertently served as the ground-ing conductor (connected to the metal case or housing of nearly any electrical appliance), and I very well remember getting shocks from metal-cased toasters, vacuum cleaners, power tools and whatever else I was trying to use if a plug was in need of being turned! It is certainly true that the equipment will work fine either way, but it used to be that the operators did not always survive!
 