Discussion in 'Plumbing Forum, Professional & DIY Advice, Tips & ' started by gmrules, May 30, 2009.

  1. gmrules

    gmrules New Member

    Messages:
    94
    Location:
    Raleigh NC
    I spoke to a local plumber ans he said that if I came ouot of the wall to a 90 horizontally and then a 90 staright up to sanitary Tee this would be considered a new combination stack and should be ok

    Here is pic of I hope my last attempt. is this correct and will I finally pass code?

    Thanks for ur help and pls be nice if I messed it up AGAIN :D It is straight the camera was on a angle

    Attached Files:

  2. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    Why all the 90's? :confused:
  3. Gary Swart

    Gary Swart In the Trades

    Messages:
    7,351
    Location:
    Yakima WA
    Sorry, you have an S trap. The problem is the tee in the drain line is too low. The tail piece from the P trap needs to go straight into the tee. The only solution I can see is to cut into the wall, cut the old tee out, and extend the drain pipe upward. Then add a new tee and adapter for the tail piece.
  4. gmrules

    gmrules New Member

    Messages:
    94
    Location:
    Raleigh NC
    The pip comes out of the wall 2" above the bottom of the cabinet so I needed to raise it up, so I put the first horizontal 90 to allow me more room to tie into the p trap. the second 90 was to raise it up.

    The pipe in the wall comes in horizontal along the wall the same way as the lower pipe I have and then turns up
  5. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    The bottowm of the trap must be below the outlet. You have an S trap there.
  6. kingsotall

    kingsotall Plunger/TurdPuncher

    That santee looks like it's pointed upwards...
  7. Redwood

    Redwood Master Plumber

    Messages:
    7,450
    Location:
    Connecticut
    The pipe in the wall...

    Does it run horizontal or, vertical?
  8. It aint pretty

    it will work but it is not pretty...
  9. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    26,679
    Location:
    Cave Creek, Arizona
    drain

    If that thing above the tee is an air admittance valve it will work, but so would coming up out of the tee without going sideways first. And just doing what you did, does not make it a combination waste and vent system. To do that would require pipe size changes and other revisions which would have been economically impractical for you.
  10. Cass

    Cass Plumber

    Messages:
    5,980
    Location:
    Ohio
    the AAV is supposed to be as high as possible...that one is to low...The whole thing is wrong but will probably work for a while...just doen't ever try and snake it...
Similar Threads: finally right
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & How can I add a p-trap to finally resolve stinky laundry room! Oct 4, 2009
Plumbing Forum, Professional & DIY Advice, Tips & 1/4 turn left or 3/4 turn right? Gas shut off valve Jun 8, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Right tool to remove circa 1951 tub drain escutcheon (1 5/8" ID) w/o cross bar? May 16, 2014
Plumbing Forum, Professional & DIY Advice, Tips & Am I laying this full bath out right Apr 14, 2014
Plumbing Forum, Professional & DIY Advice, Tips & True or False? If sweated joints don't leak right away, they won't ever leak. Mar 19, 2014

Share This Page