Delayed Ignition

Discussion in 'Boiler Forum' started by droback, Jun 6, 2009.

  1. droback

    droback New Member

    Messages:
    1
    I have a oil fired utica boiler that experience delayed starts intermittently.

    I've cleaned fully, replaced the air tube assembly (which include igniters and nozzle), and filter.

    It starts ok sometimes but at times starting is delayed causing smoke and a boom from to much oil being dumped in the chamber.

    Last time this happened (about 7 years ago), we replaced the transformer which fixed the problem.

    Is there somewhere else I should look or just replace the transformer?

    TIA
  2. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    Transformer
    Electrodes
    Nozzle
    Primary & secondary air
    Draft
    Primary control
    Solenoid valve
    Oil Pump
    Pump coupling
    Wiring problems
    Voltage problem
    Combustion chamber
    End cone
    Nozzle line adjustment