    Okay...so I posted a few days ago asking about venting a toilet with a small almost horizontal run before going vertical....Here is what we are left with....what needs to be fixed, what doesn't work...etc. Thanks guys for your honest advice!

    :)

    Jill

    [​IMG]
  2. Akpsdvan

    Akpsdvan In the Trades

    Messages:
    1,484
    Location:
    Alaska
    I might have gone with a straight run off the shower drain with a T to do the vent...

    But one works with what one has, and that is never more true than in Alaska as 95% the store is not just up the block.
  3. dcelite

    dcelite Plumber

    Messages:
    132
    Location:
    Los Gatos, CA
    We can not run a horizontal vent under the floor here. That being the case, in your situation, I would remove the 2- 3" 45 bends and install a 3"x2" combo (tee like you have for the shower). The 2" will run vertically up through the hole for the vent and then use a 3" long sweep 90 and run up to the closet flange.
  4. akantler

    akantler New Member

    Messages:
    16
    Location:
    Alaska
    Akpsdvan...that is the way we had it originally with a T as the vent, but I was gathering from folks here that I needed a combo for that vent. I did talk to the permit folks here today, and the plumbing inspector agreed. We are out of the city jurisdiction, but we still have to have a private inspector check off our work....


    dcelite...Do you mean at the horizontal area of the toilet drain, have a combo with the 2" vent...? We thought we might do that in the beginning, but weren't sure if the toilet drain could drop that far before the vent.

    Thanks guys so much for your time...
  5. dcelite

    dcelite Plumber

    Messages:
    132
    Location:
    Los Gatos, CA
    Yes. Put the combo on the horizontal 3". As long as the riser is no longer than 24" ( UPC/CPC chapter 10; 1001.4)
Similar Threads: crawlspace plumbing
Forum Title Date
Plumbing Forum, Professional & DIY Advice, Tips & indoor plumbing with no crawlspace Jan 6, 2008
Plumbing Forum, Professional & DIY Advice, Tips & 80% humidity in Crawlspace Aug 3, 2012
Plumbing Forum, Professional & DIY Advice, Tips & Is this cost estimate Reasonable? Repipe waste in crawlspace Jul 10, 2012
Plumbing Forum, Professional & DIY Advice, Tips & Methods for cleanup house drainage break water/mud from under crawlspace May 17, 2011
Plumbing Forum, Professional & DIY Advice, Tips & Crawlspace mold—drain problem?? (HELP!) Aug 3, 2008

Share This Page