Convert from zone valve to zone pumps

Users who are viewing this thread

Rockycmt

Member
Messages
166
Reaction score
1
Points
18
Location
New York Metro Area
Right now I have a 1 punp 3 zone hydro. One HW and 2 living. I want to add a radient underfloor loop via mixing valve. While doing this it seems cleaner to just do all the zones with new pumps and a 4 zone switch relay. I have the pumps already so the cost to convert is not an issue. The question I have is:

do the pumps for each zone act as valves. What I mean is... If a zone is not active and another is.... Is anything needed to isolate the zone as a zone valve does? Or will the pumps do this? (i.e. when pump is not moving it is a closed zone) All the schemas I have seen show the boiler --> pump --> zone --> boiler.

This is a nice little spring project I have planned.

Curently I have one zone running way too many radiators. 2 floors on zone, small room on zone 2, HW on zone 3.

I want to clean this up and have living spaces on 1, bedrooms on 2, Basement on 3, HW on 4.
 

Dana

In the trades
Messages
7,889
Reaction score
509
Points
113
Location
01609
You'll need a check valve in series with each pump, since the pressure differences created any one pump driving from the manifold will induce a reverse flow on the others. On very high head loops that may never present a practical issue, but on shorter hydronic loops that back flow can create unintentional heating of the "off" zones.

When reconfiguring, try to avoid micro-zones, since that causes short-cycling efficiency losses and unnecessary wear & tear on the boiler. If your current smaller zone 2 has just a low-mass stick of fin-tube for a heat emitter, it's almost certainly short-cycling on that zone. Zoning it by floors is usually pretty reasonable, as long as the room-to-room balance has been properly dealt with by load-proportional room-to-room radiation sizing (based on the room-by-room heat loads, not the square footage of the space.)
 

Rockycmt

Member
Messages
166
Reaction score
1
Points
18
Location
New York Metro Area
I understand. The Taco pumps I have have the check built in. IFC. so that should cover that.

TY for your reply it was dead on what I was looking for.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
I question whether a "4 zone switching relay" will do what you want it to, because that usually controls ONE pump and four low voltage zone valves. For your system, you will probably need four thermostats and four pump control relays, and EACH of them would need the contacts, in parallel, to operate the boiler's burner.
 

Rockycmt

Member
Messages
166
Reaction score
1
Points
18
Location
New York Metro Area
I question whether a "4 zone switching relay" will do what you want it to, because that usually controls ONE pump and four low voltage zone valves. For your system, you will probably need four thermostats and four pump control relays, and EACH of them would need the contacts, in parallel, to operate the boiler's burner.

I disagree. This is exactly what I will use.
http://www.pexsupply.com/Taco-SR504-4-4-Zone-Switching-Relay
 