conductor length
Discussion in 'Electrical Forum discussion & Blog' started by Al G., Feb 23, 2014.
  1. Al G.
    Al G. New Member
    Jul 23, 2009
    Woodbridge, VA
    I know conductors have to be long enough to extend 6" beyond the face of the wall box. Is that measured on the conductors entering the box or does it include the pigtails added for connection to the devices?
  2. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Occupation:
    Instructor
    North Carolina
    6 inches from the entry of the box and at least 3 inches on the outside of the box. Pig tails don’t count for or against this requirement
  3. Sponsor
    Sponsor Paid Advertisement
  4. Homeownerinburb
    Homeownerinburb Member
    Jan 14, 2012
    Los Angeles, CA USA
    And now we can debate the shape of sine waves!
  5. ankhseeker
    ankhseeker Member
    Oct 2, 2013
    San Pablo, California
    You have to bend the wires in a sinewave shape? Oh yeah, they need to be at least 3 cycles.
  6. Al G.
    Al G. New Member
    Jul 23, 2009
    Woodbridge, VA
    Thanks for the clarification. I thought it was 6" outside the box.
  7. jwelectric
    Jun 14, 2007
    Occupation:
    Instructor
    North Carolina
    300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points.
    At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.
    Exception: Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14.
Similar Threads: conductor length
Forum Title Date
Electrical Forum discussion & Blog Max number of conductors in 3/8 FMC Oct 19, 2016
Electrical Forum discussion & Blog Using Multi Conductor wire for heavy load May 9, 2016
Electrical Forum discussion & Blog 4 conductor to 3 conductor Jan 10, 2014
Electrical Forum discussion & Blog Derating large conductors in attic? Jul 28, 2012
Electrical Forum discussion & Blog Objections - code or otherwise of running multiple conductors Aug 26, 2011
Share This Page