Commercial water heater output

Discussion in 'Water Heater Forum, Tanks' started by ferd, Sep 15, 2011.

  1. ferd

    ferd New Member

    Joined:
    Mar 11, 2008
    Location:
    Ohio
    If I have a 400,000 btu boiler heating water into a 370 gallon tank and I change the tank out to a 120 gallon tank, how much capacity do I loose? Assuming 95% eff boiler.
     
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    What's your usage rate and temperature? Incoming water temp?
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. ferd

    ferd New Member

    Joined:
    Mar 11, 2008
    Location:
    Ohio
    output 130 deg incoming can be down to 40 boiler should put out 500 gph Just wondering what differance the tank will make.
     
  5. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego
    Round numbers, the boiler heats produces 400 gallons per hour. FIRST hour delivery is the recovery rate ( 400 gallons per hour ) PLUS 70% ot tank. SO your first hour availablilty drops from 660 gallons to 485 gallons. After the first hour, it is all recovery, 400 gallons per hour.
     
Similar Threads: Commercial water
Forum Title Date
Water Heater Forum, Tanks Does the drain fitting unscrew from water heater body? Today at 7:16 AM
Water Heater Forum, Tanks AST Storage Tank vs Indirect Water Heater vs Electric Water heater Yesterday at 3:07 PM
Water Heater Forum, Tanks hot water recirculating pump Friday at 6:37 PM
Water Heater Forum, Tanks Watts water heater expansion tank Friday at 11:20 AM
Water Heater Forum, Tanks Water heater control valve? Bradford White MI40T6FBN Jun 26, 2015

Share This Page