    If I have a 400,000 btu boiler heating water into a 370 gallon tank and I change the tank out to a 120 gallon tank, how much capacity do I loose? Assuming 95% eff boiler.
     
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Joined:
    Sep 2, 2004
    Occupation:
    Retired Systems engineer for defense industry.
    Location:
    New England
    What's your usage rate and temperature? Incoming water temp?
     
  3. Sponsor

    Sponsor Paid Advertisement

     
  4. ferd

    ferd New Member

    Joined:
    Mar 11, 2008
    Location:
    Ohio
    output 130 deg incoming can be down to 40 boiler should put out 500 gph Just wondering what differance the tank will make.
     
  5. jimbo

    jimbo Plumber

    Joined:
    Aug 31, 2004
    Location:
    San Diego
    Round numbers, the boiler heats produces 400 gallons per hour. FIRST hour delivery is the recovery rate ( 400 gallons per hour ) PLUS 70% ot tank. SO your first hour availablilty drops from 660 gallons to 485 gallons. After the first hour, it is all recovery, 400 gallons per hour.
     
Similar Threads: Commercial water
Forum Title Date
Water Heater Forum, Tanks Rebuilding shoddy boiler/hot water heater exhaust to chimney connection Apr 15, 2015
Water Heater Forum, Tanks Recommendation for new 40 gal gas hot water heater Apr 12, 2015
Water Heater Forum, Tanks When does a hot water decide to heat water Apr 1, 2015
Water Heater Forum, Tanks When is it time to replace my electric water heater? Mar 30, 2015
Water Heater Forum, Tanks Replacing a power vent water heater Mar 29, 2015

Share This Page