Coming to a Plumbing Inspector near you

Discussion in 'Plumbing Forum, Professional & DIY Advice' started by nhmaster, Dec 7, 2009.

  1. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    New and improved for 2009. The latest version of the IPC contains such nifty tidbits as this gem

    All backflow preventers having an atmospheric vent (watts 9d et al ) must have the vent piped to a waste receptor by means of an air break or an air gap.
    (those of you installing boilers should have a good time with this one)
    This includes boiler feeds and those nasty little chrome BFP's they make us put on soda machines.

    Feel the Joy Fella's

    More to come when the dust dies down. :eek:
  2. hj

    hj Moderator & Master Plumber Staff Member

    Messages:
    27,032
    Location:
    Cave Creek, Arizona
    valves

    RPPBFP valves, such as the stainless steel ones used for soda machines, have tappings for an air gap funnel. Others do not and providing one would be difficult or impossible, which is why their instructions specify that they MUST be installed in areas where a discharge would not cause damage.
Similar Threads: Coming Plumbing
Forum Title Date
Plumbing Forum, Professional & DIY Advice Hello from Simply Plumbing and lower your energy consumption for the upcoming seasons! Oct 13, 2014
Plumbing Forum, Professional & DIY Advice Ants coming in via plumbing pipe opening Jan 31, 2012
Plumbing Forum, Professional & DIY Advice Commercial Plumbing (Restaurant) repair problem--hot water coming out ice and urinal Dec 3, 2010
Plumbing Forum, Professional & DIY Advice gutter lip missing, water coming down between wall and gutter Aug 18, 2014
Plumbing Forum, Professional & DIY Advice Sewer smell coming from air conditioner drain. Jul 14, 2014

Share This Page