Combustion order from water heater fan

Discussion in 'Water Heater Forum, Tanks' started by paulcat, Dec 3, 2010.

  1. paulcat

    paulcat New Member

    Messages:
    1
    Location:
    erlanger, ky
    This seems to happen only during the winter time. The vent on top of the WH has a somewhat open back side and I can feel a draft coming out of this opening instead of up through the vent pipe and my basement fills with a strong combustion odor. Now if I open my glass sliding door in the basement, the air then goes out the vent and the smell disappears. Any advice? Could it have something to do with my furnace air flow since this only happens in the winter? My furnace is only a few feet from the WH. My basement is a very open environment, also. Thanks for any help.
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,266
    Location:
    New England
    Combustion devices actually can suck a lot of conditioned air out of a house. In the process, they suck unconditioned air in the house. The newer devices use closed combustion, where the burner gets all of its combustion air from outside, and then dumps the exhaust there as well. So, basically, combustion devices rely on sucking air in from outside to burn properly. It's better to do this in a controlled manner rather than have it do it through all of the cracks in the house. If the house is tight, it becomes worse, the device won't work right. By that, one possibility is incomplete venting - dumping it in the house rather than outside. Or, if there's not enough air, make some CO rather than CO2, which could kill you. If you don't have one, suggest you get yourself a CO detector and use it. You may need to provide an outside air vent to the area where the burners are.
  3. Thatguy

    Thatguy Homeowner

    Messages:
    1,459
    Location:
    MD
    Probably 'cause cold air sinks. You may need a draft inducer. Also, with 3 CO detectors you'll have aircraft reliability, 99.9999%, the so-called "six-nines".

    Some of your brain cells have already died if you smell that odor or if your eyes smart. With nausea and headaches, flu-like symptoms, you are close to dying. One of my customers had that, and survived.
  4. Dana

    Dana In the trades

    Messages:
    2,986
    Location:
    01609
    Flues open to the basement would normally put the basement under negative pressure from the "stack effect". Opening the slider allows outdoor air in to relieve that pressure differential, and the air/combustion exhaust to flow up the flues as-designed. But if there are other induced- exhaust points (kitchen/bath fans, or clothes dryers), it can create sufficiently negative pressure when the slider is closed that air comes down the flues, a condition called "backdrafting".

    Backdrafting combustion appliances are a serious health hazard- take this deadly-seriously!

    If there is a powered draft-inducer on the furnace it may be THE problem (and not the usual backdrafting) since the forced draft of the furnace would pressurize the flue forcing some of it's exhaust into the basement. If the furnace is atmospherically drafted, adding power draft inducer just on just the hot water heater could create reversed draft problem at the furnace whenever the hot water heater is running.

    Is the furnace a forced-draft version?

    Almost all 83%+ furnaces & boilers are induced draft, and should never share a flue with an atmospheric-drafted hot water heater. Do the furnace & hot water heater share a flue, or are they on separate flues?

    If they're both atmospheric-drafted and share a flue, sometimes adding 4-5' to the top of the chimney is enough. Alternatively, a turbine-vent or venturi-vent chimney cap can often do the trick.

    Sometimes the flue has too large a bore for the BTU rating(s) of the burner(s) attached, and would draft better with a narrower-bore liner installed.

    Properly diagnosing the cause may lead to different "right" solutions depending on the particulars.
Similar Threads: Combustion order
Forum Title Date
Water Heater Forum, Tanks Sealed combustion (powered direct-vent) water heater Nov 4, 2014
Water Heater Forum, Tanks Can I Draw Exterior Combustion Air In For My PowerVent Water Heater? Jan 21, 2010
Water Heater Forum, Tanks Hmmm waterheater venting ok but still getting exhaust/combustion smell in cellar? Dec 8, 2009
Water Heater Forum, Tanks 6 Year vs. 12 Year (plus canceled Whirlpool and ordered Bradford White) Apr 9, 2013

Share This Page