Combining vents. Please proof my layout.

Users who are viewing this thread

whackit

In the Trades
Messages
32
Reaction score
0
Points
6
Location
Los ANgeles
Hi All.

I am designing my vent system and want to have a single roof exit. Here is how it all lays out. I know I have 4" in and 4" out but just wanted to make sure everything else was okay in the middle that was combined. Assume everything else is correct (level over flood rim etc).

Thanks!
 

Attachments

  • Screen Shot 2014-06-06 at 5.47.19 PM.jpg
    Screen Shot 2014-06-06 at 5.47.19 PM.jpg
    32.9 KB · Views: 432
Last edited:

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
The ONLY ones that count are the ones connected DIRECTLY to the 4". That being the case, you have three 2" ones and one 1 1/2". That gives you an area of 3.56 times Pi, while the 4" line is 4 times Pi, so technically, you are a little shy of the requirements, but the inspector might not do the calculations.
 

whackit

In the Trades
Messages
32
Reaction score
0
Points
6
Location
Los ANgeles
The ONLY ones that count are the ones connected DIRECTLY to the 4". That being the case, you have three 2" ones and one 1 1/2". That gives you an area of 3.56 times Pi, while the 4" line is 4 times Pi, so technically, you are a little shy of the requirements, but the inspector might not do the calculations.

Thanks for the reply. I can break out another 1.5 vent pretty easily so that will get me to the right number. I was mostly concerned about the large group on the left that all combines through a single 2" line. I wasn't sure if I would be allowed 2 toilets on a single 2" line. I did the DFU calks and that gives me a total of 18 (i forgot a floor drain on the drawing) and the California code book says I am allowed 24 on a 2" line so I guess that's fine too.
 

Kiton

Member
Messages
88
Reaction score
5
Points
8
Location
Quebec
HJ, how does this get calculated? What is the ideal or required
 
Last edited by a moderator:

Terry

The Plumbing Wizard
Staff member
Messages
29,946
Reaction score
3,460
Points
113
Location
Bothell, Washington
Website
terrylove.com
In California, using UPC plumbing code, you can run three bathrooms on 2"
However, you do need 4" through the roof if you have 4" going down. A four bath home used 4" when the forth toilet is added.

You can achieve the 4" area by also using four 2" vents.
In this case, he just ones a single 4" vent.

dwv_b2.jpg
 

Kiton

Member
Messages
88
Reaction score
5
Points
8
Location
Quebec
My high school math tells me: Area = pi x radius2.

So HJ is comparing the squared radii prior to multiplying by pi.

I was referring to code requirements and application of, I was told that locally, the only thing that counts was the vent could not be smaller than half the size of the largest pipe it serves in the system. That appears to be an over simplification.


However, you do need 4" through the roof if you have 4" going down.


We generally have a 4 inch servicing the bathrooms and a separate 2 inch servicing the kitchens so I was curious about Whackit's config.
Thank you,
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; HJ, how does this get calculated? What is the ideal or required

In most cases, the total AREA of the pipes through the roof should be the same or greater than the area of the incoming sewer line. The simplest way to do the calculation is to take half the diameter of the pipe, square it, do the same to ALL the germane vent lines. Add those numbers together and compare the answer to half the diameter of the main drain squared. Do NOT factor in PI because it is a constant and cancels out.
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
quote; So HJ is comparing the squared radii prior to multiplying by pi.

You are NOT interested in the actual area, you are making a comparison, and for that calculation, since PI is a constant and cancels out it can be ignored.
 

Kiton

Member
Messages
88
Reaction score
5
Points
8
Location
Quebec
In most cases, the total AREA of the pipes through the roof should be the same or greater than the area of the incoming sewer line. The simplest way to do the calculation is to take half the diameter of the pipe, square it, do the same to ALL the germane vent lines. Add those numbers together and compare the answer to half the diameter of the main drain squared. Do NOT factor in PI because it is a constant and cancels out.


Thank you hj,
 