Have a question with this existing section shown in picture. It is 3 inch copper DWV handling a water closet, sink and shower upstream. The shower and sink tie in with 2 inch copper and is a wet vent combination. The 3" wye shown does not have the opening to match 4" XH pipe going out. The sump pump was pipe to go out thru 2" front hub.
What I would like to do is remove this section including 3" wye and spigot area, then replace with Charlotte cast iron 4" wye w/ 2" right hand side outlet. The 4" wye would have a cleanout with 3 1/2 brass plug and sump pump would be piped into the 2" outlet side. The before and after shown in picture.
Would this be code acceptable.
Thanks, Johnnymac
What I would like to do is remove this section including 3" wye and spigot area, then replace with Charlotte cast iron 4" wye w/ 2" right hand side outlet. The 4" wye would have a cleanout with 3 1/2 brass plug and sump pump would be piped into the 2" outlet side. The before and after shown in picture.