I have a 1/2 hp 10 gpm pump in my 4000 gallon cistern. When the pressure switch activates the breaker trips. This pump is protected by a pumptec which does not trip.
I OHMed the pump and it measured 5 ohms, normal for this pump.
I switched the breaker with the one from the deep well, (same amps). It tripped as well. The tripping is immediate.
I bypassed the pumptec electrically and it tripped similarly.
Where do I look next? It seems to me that the breaker, pumptec and switch are good. If the pump trips the breaker but ohms correctly, could it still be bad?
The pump is 8 years old and there is a cycle stop valve before the pressure switch.
Any advice welcomed and appreciated.
BTW. We are bypassing the cistern and using the wells directly so we have water, just not enough to irrigate.