    can a one inch swing check valve be placed in a vertical pipe and still worK? Or do they have to be horizontal?

    It's for near-boiler piping, to prevent domestic hot water heater usage improperly getting hot water to the house hydronic system in summer
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    21,990
    Location:
    New England
    A little more info would be required. There should not be any cross-coupling between hydronic and potable water. Do you have say a demand type system in your boiler you shut off for the summer and use a tank instead? I'd consider just using a valve(s) to shut one off and open the other.

    Check valves can (normally) go horizontal (properly oriented) or vertical. If this is for potable water, you'll need probably a bronze, SS, or plastic approved for potable water use. Being hot may create some other problems.
  3. msgale

    msgale New Member

    Messages:
    90
    Location:
    Ohio
    this is for the water heated by the mod-con boiler in a hydronic system. Now, its a primary/secondary set of loops, one zone only.

    The revision is to add an indirect water heater. For summer use of the water heater, i need check valve to protect against boiler-heated water going thru the house radiators.

    none of this is potable water. the heated hot wster for human use is on a separate set of pipes
  4. kingsotall

    kingsotall Plunger/TurdPuncher

    Indirect water heater. Check valve goes after DHW pump before the tee where the return from the sysytem goes into the boiler. On the verticle is fine with a swing check.
    Might want to wait for Thatguy, nhmaster or HJ to weigh in with their opinions.
  5. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    What you need is a flow check valve which is not like a regular swing or ball check in that it has a weighted gate. Check out www.taco-hvac.com What you probably want is a Taco 219.
  6. msgale

    msgale New Member

    Messages:
    90
    Location:
    Ohio
    i can't find 219 in taco, is ther another name?

    tried the web site, no luck
  7. msgale

    msgale New Member

    Messages:
    90
    Location:
    Ohio
    OK, found the 219...

    How is that different or better than a plain swing check valve?
  8. nhmaster

    nhmaster Master Plumber

    Messages:
    3,189
    Location:
    S. Maine
    The check in a standard swing check is not heavy enough to always stay closed against thermal migration. A flow check has a heavier check assembly.
  9. msgale

    msgale New Member

    Messages:
    90
    Location:
    Ohio
    ok, sounds reasonable, thank you , all of you, for the info.
    I love this board
Similar Threads: check valve
Forum Title Date
Boiler Forum Replacing old NG boiler / water heater - check my sizing please? Sep 6, 2014
Boiler Forum Can someone check my Math and help with calculation? Dec 6, 2013
Boiler Forum Check please!!! Sep 10, 2013
Boiler Forum 35+ PSI boiler pressure. Have gone through the usual checks. May 29, 2013
Boiler Forum Zone valve about to die? May 29, 2014

Share This Page