    hello all,
    I have had great advice from this site and I need it again.
    I have a two wire outlet in the attic . I have guitar amp that I want to put there. The amp has three prongs . Since running a ground to the water pipe is near impossible. But I know that I can put in a gfi outlet with "no equipment ground" . Can I put a 14 ga single wire from the ground screw on the outlet to the white neutral screw will that provide equipment ground?. Or is it code for massachusetts? Please help!!!!
  2. jimbo

    jimbo Plumber

    Messages:
    8,997
    Location:
    San Diego
    Whoa! Nope...can't do that!
  3. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,055
    Location:
    New England
    The whole idea of the safety ground is to have a TOTALLY independent safety path back to the breaker/fuse panel to ensure that the breaker/fuse will trip if there is a short. A jumper between the neutral and ground would NOT perform this safety feature. Use a GFCI recepticle, if you must emulate a ground there, or rewire the whole circuit. The GFCI essentially does the same thing, but electronically, rather than mechanically.
  4. danl02026

    danl02026 millwork specialist@home depot

    Messages:
    9
    Location:
    dedham,mass
    two prong to three

    thank for the info ==I tried the gfi outlet but I was getting to much hum. I have used this setup in other settings . I guess Im pulling wires for the weekend...again thanks
Similar Threads: change prong
Forum Title Date
Electrical Forum discussion & Blog Service Panel Change Out.. Need Help Determining and Sizing Panel May 28, 2013
Electrical Forum discussion & Blog ROMEX®/cable color changes Sep 21, 2011
Electrical Forum discussion & Blog Using just a screwdriver to change out a 100 amp main panel to a new 200 amp panel May 7, 2010
Electrical Forum discussion & Blog GFCI Outlet change Sep 26, 2009
Electrical Forum discussion & Blog Open Ground after change to GFCI Jul 28, 2009

Share This Page