What is causing my CH inlet filter to blow out the bottom of my wall mount combi boiler? I ran the system for five days then it blew out. Am I running the pump speed too fast? Should I look at check valves/ remove? Not sure what I am doing wrong
 

NY_Rob

In the Trades
Messages
317
Reaction score
26
Points
28
Location
New York
Post some of the photos you attached in the thread you have going over at Heating Help:
http://forum.heatinghelp.com/discussion/157839/ch-inlet-filter#latest

But, looking at the attached photo from The Wall thread- the valve to the left of the circulator pump flange valve should probably be opened- not closed as it is in your photo. Closing that valve with the pump running could blow out the strainer/filter.

Maybe post some photos with the valve handles in their current positions....



e1c17a46e64941442dfa3ad66e119f.jpeg
 