Can you drain a washing machine (only) with 1 1/2'' pvc , my inspector says it must be 2'' ?
sawhorse
Illinois
Code says laundry machine has a load value of 2(DFU) and a 1 1/2 pipe has a load rating of three so why a 2 inch pipe ?
Many newer washers pump the water out faster, so hence the code thing. 1.5 may or may not work OK with your washer.
Cool Blue Harley
One Dumb Plumber
San Francisco, CA
Clothes washers are normally rated at 3 DFU each. Clothes washers in a battery of three or more are rated at 6 fixture units when sizing the common horizontal and vertical waste pipe sizing to take into account the possibility of simultaneous discharge and the suds producing effect in the drainage piping.
A 1&1/2 inch pipe is rated at 2 DFU vertical and 1 DFU horizontal.
A fixture unit is a numerical load factor which measures on some select scale the load-producing effects of a single plumbing fixture of a given kind.
It makes no difference whether a 1 1/2" line can drain the washer, because you are not going to get it approved until you satisfy the inspector. But, almost, if not all, codes do call for at least a 2" drain for a washer.