BTU Help

Discussion in 'Water Heater Forum, Tanks' started by achaean27, May 2, 2013.

  1. achaean27

    achaean27 New Member

    May 2, 2013
    I have an application where I need to consume 20 gallons of hot water every 8 minutes for a total of 7 times (for a commercial washing machine). The temperature needs to be 160 degrees Fahrenheit for each fill. What size commercial water heater would I need to get to make this work? Below is what I think would work...

    75 Gallon Rheem Commerical Water Heater @ 75,100 BTU (recovery rate is 75.8 gallons per hour)

    Can someone confirm?
  2. DonL

    DonL Jack of all trades Master of one

    Mar 30, 2011
    Rocket Scientist
    Houston, TX

    That sounds close. You would need to enter the incoming water temp into the equation to get a closer answer.
  3. Sponsor

    Sponsor Paid Advertisement

  4. nukeman

    nukeman Nuclear Engineer

    Nov 20, 2009
    Nuclear Engineer
    I assume by the "total of 7 times", you mean 7 times per hour??

    Assuming this thing is going to actually be feeding 20 gallons every 8 minutes (all day), it would be best to ignore the inital stored volume and concentrate on what the burner can produce.

    So, if this thing is working full time, we can assume 20 gal/8 minutes = 2.5 gpm (~20 lbm/min)

    Next, you need to look at your temperature rise. During the summer, you are looking at probably 100F rise (160F - 60F). In winter, you may be more like 120F or 125F rise.

    1 BTU will raise 1 lb of water by 1 F.

    So, 20lbm/min x 125F rise = 2500 BTU/min or 150,000 BTU/hr

    This means if you have 150,000 BTU (output) you will never run out of hot water assuming nothing else substantial is tapping into this tank at the same time.

    Now, if this think isn't going to run back-to-back or you have more time between loads, you can get by with a smaller burner. You could also potentially go with two tanks (with say 75k burners) instead of a single tank with a huge burner.
  5. Dana

    Dana In the trades

    Jan 14, 2009
    Some commercial washing operations have also been able to reap a real performance boosts from drainwater heat recovery heat exchangers, provided that there is some drain flow concurrent with filling. For a single batch fill/drain later it doesn't work, but for multiple washers running staggered timing it can be very cost effective. The ideal is a fully balanced flow (say in a shower, where the drain flows for over 95% of the period that the hot water is being drawn), but big operations with many washers, there's a strong temporal overlap, if not 90%+. It's some thing that has to be designed, for a commercial app, unlike a residential shower.

Similar Threads: Help
Forum Title Date
Water Heater Forum, Tanks New Homeowner .. Need help with a new water heater Sep 26, 2015
Water Heater Forum, Tanks GE Powervent GG50S06RVK Water Heater help? Sep 14, 2015
Water Heater Forum, Tanks Hot water heater help! Aug 15, 2015
Water Heater Forum, Tanks Need help/reassurance my hot water tank is safe Jun 24, 2015
Water Heater Forum, Tanks Help! fuse keeps blowing May 25, 2015

Share This Page