Breaker tripping
Discussion in 'HVAC Heating & Cooling' started by envycycles, Jul 17, 2013.
  1. envycycles
    envycycles New Member
    Jul 17, 2013
    FL
    Hey whats up guys
    Trying to see if I can get some help here. I have read a lot and done some testing but need further help.
    So my outside breaker was found tripped, reset it and once the outside unit come on it trips again.
    So with the breaker in and no AC requested I checked the contactor in and it shows 240V on the input side.
    I took off the run capacitor which its a 40uf and drained it and checked it and it says 36uf between the herm and C and about 5uf between the herm and fan or fan and C.
    I took of the start capacitor because it had leaked out but the plug was still in. Took the bleeding resistor off and checked it was getting some crazy numbers 39.97n. I ordered a new one and when it came in I checked it and it showed 155.5uf so I know this one is good. I soldered the same 15ohm resistor to it and then installed and reset the breaker and still the same thing happened. Breaker trips.
    Today I disconnected the leads that come from the compressor to the contactor and the capacitor and activated the contactor and the fan started with no issues and no breaker trip.
    I have not noticed any humming sound from the compressor.
    Read that to check the compressor I have to remove the leads from the comp and check them to ground and if it beeps then the compressor is shot. My question on this is can I check the leads coming from the comp to the contactor instead of removing the whole top cover and fan?
    Also any way to check the start relay and also the contactor?
    Im pretty handy as Im a Aircraft tech so Im willing to check what ever needs to be checked to avoid having to pay. If the compressor needs to be replaced then I will call a Pro.
  2. DonL
    DonL Jack of all trades Master of one
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    If you have a 15 ohm bleeder resistor, then that sounds wrong.
    Your description of 155.5uf has me a bit confused, if it should be a 40uf cap. I may have misunderstood.
    Does the Breaker trip, just as soon as it starts or tries to run, or is there a delay before it trips ?
    You should have no continuity from the compressor frame to the start and run windings, when the compressor is disconnected.
    What Model are you working with ?
    Good Luck.
  4. envycycles
    Jul 17, 2013
    FL
    The resistor is a 15K Ohms
    The start capacitor is a 135-155uf and the dual cap is a 40uf.
    The breaker trips when i turn on the thermostat and request a/c.
    Its a Trane XE1200 unit(TWP036C100A3), looking at my papers the comp should be a Climatuff 200/230/1/60 L.R AMPS 15.2-91
  5. DonL
    Mar 30, 2011
    Rocket Scientist
    Houston, TX
    It would be good to use a Amp Probe to locate the problem.
    Look at the Compressor heater current, and motor winding currents.
    I did not see a manual online for that unit, but it should be fairly easy to troubleshoot.
    Don't rule out that it may have a problem in the controller, If for some reason it is trying to turn on Heating Elements and the Compressor at the same time. That can trip a breaker.
    Good Luck.
Similar Threads: Breaker tripping
HVAC Heating & Cooling Breaker / Fuse Protection LG LMU369HV Aug 25, 2015
HVAC Heating & Cooling Goodman 1.5 ton spilt unit. Fan turns slow and breaker trips May 31, 2015
HVAC Heating & Cooling proper breaker and wire size for gas furnace Apr 14, 2013
HVAC Heating & Cooling 10kw vs 7kw heat strip w 50 amp stab-loc breaker. Advice needed Mar 2, 2013
HVAC Heating & Cooling Thermostat, Breaker, unit?? Jan 20, 2012