Breaker tripping

Discussion in 'Pumps and Tanks Well Forum & Blog' started by Ben47, May 6, 2013.

  1. Ben47

    Ben47 New Member

    Messages:
    3
    Location:
    Virginia
    While watering my plants the breaker to the pump will trip at various times. It has happened four time over a period of 3 days. I have a Goulds Bruiser submersible pump, Model 7SB07422C and a 50 gallon tank. The pressure switch is set to come on at 40# and go off at 65#. It cycles at about 33 sec- 15 sec on, 18 sec off (which seems fast to me) with the hose bib putting out about 3/4 volume. What things could cause the breaker to trip?
  2. valveman

    valveman Moderator Staff Member

    Messages:
    4,347
    Location:
    Lubbock, Texas
    Running for 15 seconds and off for 18 seconds is what is causing the breaker to trip. That is very fast and probably means you tank isn’t holding the 12-14 gallons it should. The bladder in the tank is probably bad, and that is also caused by cycling the pump on and off. Pumps like to run 24/7. Cycling on and off destroys everything in a pump system.
  3. craigpump

    craigpump Member

    Messages:
    839
    Location:
    ct
    The windings in the motor are overheating and eventually the motor will quit. Like valveman said, it sounds like the bladder has gone bad in the tank. Time for a new tank....
  4. Ben47

    Ben47 New Member

    Messages:
    3
    Location:
    Virginia
    Thanks. Both the pump and tank are only 6 months old and have been used rarely as the house is still being built. Very strange.
  5. VAWellDriller

    VAWellDriller New Member

    Messages:
    170
    Location:
    Richmond, VA
    All should be under warranty then....call the installer back.
  6. valveman

    valveman Moderator Staff Member

    Messages:
    4,347
    Location:
    Lubbock, Texas
    Even with a fairly new tank the bladder gets lot of abuse from the pump cycling on and off. And 2 wires motors are the worst for tripping a breaker when they cycle on and off too much.
  7. DonL

    DonL Jack of all trades

    Messages:
    3,810
    Location:
    Houston, TX
    If you have a temporary electrical service for your house being built, you may just have excess voltage drop.

    A volt meter and amp probe will show you the problem. The breaker could be to small for the motor if the voltage is correct at the pump motor.

    Or the wire gauge is to small for its length.

    What size breaker and wire are you using ? What voltage are you using ?


    Good Luck.
    Last edited: May 7, 2013
Similar Threads: Breaker tripping
Forum Title Date
Pumps and Tanks Well Forum & Blog Tripping breaker May 22, 2012
Pumps and Tanks Well Forum & Blog Circuit Breaker tripping after constant cycling Sep 22, 2010
Pumps and Tanks Well Forum & Blog Gould jet pump humming tripping breaker Aug 6, 2010
Pumps and Tanks Well Forum & Blog Well water pump tripping circuit breaker Jun 7, 2010
Pumps and Tanks Well Forum & Blog circut breaker tripping need help!! Jul 20, 2009

Share This Page