Boiler not operating within Hi Lo limits

Discussion in 'Boiler Forum' started by ut7351a, Dec 7, 2010.

  1. ut7351a

    ut7351a New Member

    Messages:
    2
    Location:
    PA
    I have a Teledyne Laars Max D100 Boiler w/ indirect hot water. It is a cold start boller. It has separate Hi Lo limit controls. Hi limit set at 200F, Lo limit set at 180F. Problem: When thermostat calls or heat, boiler heats up to about 165F & burner cuts out. As water circulates boiler temp starts to drop. When boiler temp drops to about 155F, burner kicks back in & heats up to about 165F again & continues back & forth until thermostat is statisfied. Why isn't boiler operating between the Hi Lo control settings?
  2. jadnashua

    jadnashua Retired Defense Industry Engineer xxx

    Messages:
    22,023
    Location:
    New England
    Does it have an outdoor reset controller? If so, it adjusts to the load and outside temperature and overrides the manual settings.
  3. ut7351a

    ut7351a New Member

    Messages:
    2
    Location:
    PA
    No Outdoor controller.
  4. Dana

    Dana In the trades

    Messages:
    2,848
    Location:
    01609
    This boiler probably has a safety high-limit aquastat in addition to the operational high/low settings. If the safety is set (or has failed) to 165F (lower than the operational high limit) it would exhibit this sort of behavior- kick off at 165F, back on again at 155F, repeat...

    Is this the boiler in question?

    If it's this series or similar and you incorrectly assumed the safety aquastat to be the low-limit, that could be the whole issue. (although 165F is way lower than the 180F you set it to.)

    What model aquastat(s) does this beast have?
Similar Threads: Boiler operating
Forum Title Date
Boiler Forum Hydronic System Design & Boiler Piping/Control Wednesday at 6:23 PM
Boiler Forum Help Replacing an Old Boiler Sep 14, 2014
Boiler Forum Replacing old NG boiler / water heater - check my sizing please? Sep 6, 2014
Boiler Forum Combi-Boiler NCB 240 (Navien) Sep 5, 2014
Boiler Forum Nat. Gas Boiler Selection Aug 24, 2014

Share This Page