Bath rough-in

Users who are viewing this thread

rdcusmc

New Member
Messages
3
Reaction score
0
Points
0
How's this look? Toilet, shower and sink drain. Shower and sink on 2 inch common wet vented to the stack before the 3 inch toilet drain.

Will fine tune support straps prior to gluing this up. Anyone see any problems prior to applying glue???

Thanks in advance!

Ron

http://www.flickr.com/photos/38986041@N07/sets/72157618992774175/

rdcusmc
 
Last edited:

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
With your elevation change prior to the lavatory I think you need to add a vent for your toilet.
 

hj

Master Plumber
Messages
33,602
Reaction score
1,039
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
drains

The toilet and shower are NOT vented, at least not vented properly, and I doubt that few inspectors would approve that offset shower drain, OR the notches in the bottom of the joists, especially since NEITHER of them was necessary.
 
Last edited:

rdcusmc

New Member
Messages
3
Reaction score
0
Points
0
Thanks for your reply. As for the notch, the joists are 2x10 on 12 inch centers and cross-braced - no worries on weakening the floor or pipe clearances to allow for movement.

As for the layout, I read an earlier post by Terry stating this layout worked as long as the shower/lav connected downstream of the toilet. If this is not correct, will adding the toilet vent make this workable?

Thanks,
Ron
 

hj

Master Plumber
Messages
33,602
Reaction score
1,039
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
vents

You must have missed the part where the vents have to be within a specific distance from the shower trap, and the toilet opening, and both of these are too far away in your design. Adding a toilet vent would not help the shower either. Regardless of the joist size and spacing, neither notch was necessary if the piping had been arranged differently.
 

rdcusmc

New Member
Messages
3
Reaction score
0
Points
0
Maybe I read the wrong info. My understanding was that the shower and toilet were OK as long as they were within 5' of the main which they are (exactly 4' distance).

I can easily add a common vent to connect the shower and toilet run back up through the wall and connect over to the vent stack above the lav. Would this work?

Thanks again!
Ron
 

GutJob598

New Member
Messages
5
Reaction score
0
Points
0
Why not head off the floor joists rather than notching them?? Incredibly simple to do with some joist hangers. You've basically made the joists with the notches into 2x6s. I'm pretty sure a 2x6 wouldn't cut it for the span you have there.

Your house won't fall down, but notching like that isn't right.
 
Last edited:

FloridaOrange

Plumbing Designer
Messages
1,298
Reaction score
2
Points
36
Location
SW Florida
I'm not sure about the offsets to your lav, I'll look at it further. Your shower is served by a running trap, the trap for the shower needs to be at the drain. If your lav is ok and properly vented then that can vent the shower, with the relocated trap. I still think you'll need an individual vent for your toilet due to elevation change.
 