Basic Wiring Question

Users who are viewing this thread

Jcheech

New Member
Messages
12
Reaction score
0
Points
1
Location
New York
I am planning a new circuit. It will be a 15 amp circuit running from the panel to a four gang box. The circuit will power a bathroom fan and three light fixtures.

In order to wire the four switches I'll need to make a pigtail from the line to each switch in the four gang box. That means I'll have four wires plus the line for a total of five wires in this single pigtail. Is this safe to do? Further, is it required that I twist all five wires together to make the pigtail or is it OK to align them with one another and twist a wire nut onto the end.

Just need some help with the mechanics. Thanks,

Joe
 

Speedy Petey

Licensed Electrical Contractor
Messages
1,108
Reaction score
9
Points
38
Location
NY State, USA
Your pigtail method is fine. That is exactly how I do it.

As far as twisting, that is a highly contentious issue among electricians.
Pre-twisting is not usually required, but most of us do it.

I will just say, if you do not pre-twist the wires, and you remove the wire nut after, it should look like you did twist them. Understand?
 

Jcheech

New Member
Messages
12
Reaction score
0
Points
1
Location
New York
Thanks, Pete. I'll have to practice on some scrap material first. I'm thnking it would be easier if i strip off more than 3/4" from each wire - say about 2 inches - twist them neatly and trim the whole thing down to the right length.

Regards.
 

Mikey

Aspiring Old Fart, EE, computer & networking geek
Messages
3,024
Reaction score
17
Points
38
Location
Hansville, Washington
Thanks, Pete. I'll have to practice on some scrap material first. I'm thnking it would be easier if i strip off more than 3/4" from each wire - say about 2 inches - twist them neatly and trim the whole thing down to the right length.
Good idea. I hold the bundle of wires with one pair of pliers, and twist with another, then trim the twist to length, nice and neat. Lately, I've been using some push-in splice blocks that I'm really beginning to like, especially for big bundles -- they come in up to eight-hole versions.
Ideal push-ins.jpg
 

hj

Master Plumber
Messages
33,599
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
switches

I would take a piece of wire about a foot long, strip several areas along its length then loop each bare section around one of the switch terminals, then wire nut the loose end to the hot lead. Eliminating a big ball of wires and giving a tight connection at the switches.
 

Jcheech

New Member
Messages
12
Reaction score
0
Points
1
Location
New York
Thanks everyone for the input. Mission accomplished! I created 4 12-inch strands of wire, stripped off about two inches from each one and twisted them together with the line feed, then i cut it down to length and put a wire nut on it. It was nice and tight and even looked like a seasoned pro did it.

Thanks again.
 

Mattbee24

In the Trades
Messages
100
Reaction score
0
Points
0
Location
Fremont, OH
In cases like this, I prefer using the back-wired switches.(not the push-ins). You can jump from one switch to the other eliminating the "mess" of all that extra wire in the box.
 