Tankless water heater with dedicated recirculation line and pump (Rinnai). Water line from heater to farthest faucet (kitchen) is 3/4" CPVC, and then the recirculation line is a straight run of 1/2" PEX back (about 40-50').
Heater is set at 130 deg.
The symptom I am seeing is our master bathroom shower never seems to get above about 115 degree (taken a thermometer) when the recirc line is open, but if I close it down, it quickly climbs up to 125 degree.
There is a check-valve on the recirc line (swing gate right after it splits off the CPVC), and then it makes its long run directly into the cold water source. About 2 feet upstream from where the recirc line comes in is another check valve (spring) protecting the cold water line.
Originally, my MBR shower was plumbed not on the main recirc loop, and I thought that was the issue, so I took some time yesterday and redid it where the first fixture now after the heater is the shower (about a 4' 1/2" branch to the shower from the main trunk).
That did not seem to fix it.
The tankless will also show me the waterflow through it, and when the shower is on, and the recirc line is open, it is 1.5GPM, but when I close the line (and the temp at the shower jumps), the waterflow through the heater increases to 1.8 GPM.
So, my theory is that the recirculation line is giving a path of very little resistance and hot water is being diverted from my shower and into the loop -- such that the tankless is drawing a decent portion of its "source" water from the recirculation line, and not from the cold water line (by my calculations, about 30%).
Originally my plumber had a swing gate check valve on the cold water line by the heater, but it was fairly loud, so he replaced it with the spring one. I don't remember this being an issue before the change, but I can't be positive, because I just started measuring the water temp exactly.
Is it possible that the resistance on pulling from cold water line is higher now due to the spring valve, and that is allowing for more water to be pulled from the recirc line, causing the symptom?
My next step was to install another spring check valve on the recirculation line, but as close as possible to where it connects into the cold water line, with the hope that it will "balance" the resistance of both lines, and reduce the draw away from the shower.
Or am I thinking about this wrong?
Heater is set at 130 deg.
The symptom I am seeing is our master bathroom shower never seems to get above about 115 degree (taken a thermometer) when the recirc line is open, but if I close it down, it quickly climbs up to 125 degree.
There is a check-valve on the recirc line (swing gate right after it splits off the CPVC), and then it makes its long run directly into the cold water source. About 2 feet upstream from where the recirc line comes in is another check valve (spring) protecting the cold water line.
Originally, my MBR shower was plumbed not on the main recirc loop, and I thought that was the issue, so I took some time yesterday and redid it where the first fixture now after the heater is the shower (about a 4' 1/2" branch to the shower from the main trunk).
That did not seem to fix it.
The tankless will also show me the waterflow through it, and when the shower is on, and the recirc line is open, it is 1.5GPM, but when I close the line (and the temp at the shower jumps), the waterflow through the heater increases to 1.8 GPM.
So, my theory is that the recirculation line is giving a path of very little resistance and hot water is being diverted from my shower and into the loop -- such that the tankless is drawing a decent portion of its "source" water from the recirculation line, and not from the cold water line (by my calculations, about 30%).
Originally my plumber had a swing gate check valve on the cold water line by the heater, but it was fairly loud, so he replaced it with the spring one. I don't remember this being an issue before the change, but I can't be positive, because I just started measuring the water temp exactly.
Is it possible that the resistance on pulling from cold water line is higher now due to the spring valve, and that is allowing for more water to be pulled from the recirc line, causing the symptom?
My next step was to install another spring check valve on the recirculation line, but as close as possible to where it connects into the cold water line, with the hope that it will "balance" the resistance of both lines, and reduce the draw away from the shower.
Or am I thinking about this wrong?