Bad Zone Valve - boiler
Discussion in 'HVAC Heating & Cooling' started by Smokin', Oct 28, 2008.
  1. Smokin'
    Smokin' New Member
    Oct 28, 2008
    TC MN 'burb
    So I call out my utility company who put in the new boiler 3 years ago - I'm out of warranty and on a service plan BUT the zone valve is not a covered item.:mad:
    So I ask - how do you recommend and get a "call around" reply. Sheesh - they picked us clean for $6700 on the boiler and now this. I'm learning the game......
    It's a Honeywell valve - how hard are these things to replace at that? I can get one for $119 locally and willing to try it I guess. It's 24 this am - heat shall be needed for the next 7 months:eek:
  2. Furd
    Furd Engineer
    Jul 3, 2007
    Retired energy systems engineer
    Wet side of Washington State
    More than likely it isn't the entire valve that needs replacing but just the power unit.
    I'm not familiar with the Honeywell zone valves but often you can replace the power unit without even shutting down the system. It could also just be a wiring fault.
    Somewhere on your valve there is a manual lever or wheel that will allow you to open the valve manually. Try this and see if you get heat.
    Pictures of the valve and also the boiler with its nearby piping might help us to help you.
  4. Smokin'
    Smokin' New Member
    Oct 28, 2008
    TC MN 'burb
    Okay - I'll snap a few shots and post in a bit. The valves were also new when they put in the boiler so I hope the power unit can be a swap out easy.
    When I fire up the other 2 zones and move the lever it seems that it vibrates - I don't know for sure if it gets hot to outflow pipe tho - never left all zones open for more than a few minutes before since it was warm. Different story now:(
    I'll snap some shots when I get home and try to figure out how to post them here. Thanks for the advice and help!
Similar Threads: Zone Valve
HVAC Heating & Cooling Taco zone valve coming loose Dec 16, 2015
HVAC Heating & Cooling Adding Zone valves to Honeywell Aquastat L8148J Mar 6, 2014
HVAC Heating & Cooling Wiring 4-6 Zone Valves into Argo 20KW Electric Boiler. Do I need a control box ? Nov 8, 2013
HVAC Heating & Cooling Problem with Honeywell hydronic zone valve--replacement the only option? Jan 28, 2013
HVAC Heating & Cooling Convert from zone valve to zone pumps Jan 2, 2013