Avoiding S-trap

Users who are viewing this thread

FlashPD

New Member
Messages
7
Reaction score
0
Points
0
Location
TN
During remodel, plumber installed waste pipe for vanity sinks. The pipes run vertically through the floor instead of through the wall with a stub out. This means I will have to cut holes for waste pipe and supply lines in the bottom of my cabinet. That will be a pain, but the major problem is code prohibits S-traps. How do I connect a P-trap to vertical pipe without making it into an S-trap?
 

hj

Master Plumber
Messages
33,600
Reaction score
1,037
Points
113
Location
Cave Creek, Arizona
Website
www.terrylove.com
trap

You can't but if your code allows air admittance valves, you can install a tee in place of the elbow and then install the AAV on top of a short pipe riser. Then a conventional "P" trap would fasten to the side inlet of the tee.
 