Advice needed, problem with short wires in box
Discussion in 'Electrical Forum discussion & Blog' started by apparentgenius, Dec 21, 2008.
  1. apparentgenius
    apparentgenius New Member
    May 5, 2008
    Oregon
    In my never ending remodeling projects, I am in the process of adding a couple of recepticles to my existing kitchen circuit. It is a 20A circuit and only has 2 single receptacles on it now and I am changing them to duplexes.
    The problem is that the wires in the boxes were trimmed very short, they extend maybe an inch or so beyond the boxes, don't ask me why, it is just how they are. Can I add a pigtail to these to give myself sufficient working length extending beyond the box or is it necessary to pull new wire to remedy this situation (would be a real pain). I guess my basic question here is "do all wire ends need to extend the minimum distance from the box or just the ones connecting the device at that box"?
    Having recently wired my vacation home in the same county, the inspector pulled a "sample" recepticle to check my work, including the length of the wires, so I imagine he will do the same here.
    Thanks in advance.
    Glen
  2. jwelectric
    jwelectric Electrical Contractor/Instructor
    Jun 14, 2007
    Instructor
    North Carolina
    300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points.
    At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening.
  4. Thatguy
    Thatguy Homeowner
    Aug 27, 2008
    A bounty hunter like in "Raising Arizona"
    MD
    I'd solder longer wires onto them and use heat-shrink tubing to cover the (hook) splice.
    The copper needs to be lightly sanded first so the oxide is removed.
  5. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    do what did you say???????????
    No! No! No!
    Never solder a conductor never
  6. Thatguy
    Thatguy Homeowner
    Aug 27, 2008
    MD
  7. jwelectric
    Jun 14, 2007
    Instructor
    North Carolina
    I think the question is, "what is code compliant as the inspector is going to look at them"
    The only code compliant way is to replace them wouldn't you say?
  8. Alectrician
    Alectrician DIY Senior Member
    Jun 15, 2007
    If they are 1" out of the box you have enough (barely) to work with and pigtail them.
    You might try to loosen the box clamps (if any) and see if there is any slack in the wall. You can also (sometimes) relocate the box up or down to get more wire. No inspector is going to turn down a repair like that. New installation and repair generally have different criteria.
  9. jar546
    jar546 In the Trades
    Feb 20, 2008
    USA
    Contact the electrical inspector and tell him/her what the situation is and ask what is required to pass inspection. That is the safest bet.
    If you were in my jurisdiction I would allow you to pigtail as long as they were all done neatly and in a workman like manner. AHJ call.
  10. apparentgenius
    May 5, 2008
    Oregon
    Everyone,
    Thanks for the advice and clarity on the code. I'll give the inspector a call and see if he lets me go the pigtail route. Might as well ask before pulling new wire.
    Glen
  11. maintenanceguy
    maintenanceguy In the Trades
    Aug 18, 2008
    Pennsylvania
    This is so obvious that I'm sure you've already thought of it but is there enough slack in the wires to pull another couple of inches into the box?
  12. GabeS
    GabeS Remodel Contractor
    Jan 10, 2007
    Remodel contractor
    Brooklyn NY
    That has already been suggested.
Similar Threads: Advice needed
Electrical Forum discussion & Blog Advice Needed - House with old school low voltage GE system May 1, 2012
Electrical Forum discussion & Blog VERY annoying electrical problem - cannot figure out - Pro advice needed Sep 3, 2010
Electrical Forum discussion & Blog Advice for wiring 2 baseboard heaters Dec 16, 2016
Electrical Forum discussion & Blog Advice on feeding house panel from pole mounted meter 200a Aug 28, 2016
Electrical Forum discussion & Blog I am Moving my Meter Base and Need Some Advice Jun 9, 2016